Discuss Contactor overload in the UK Electrical Forum area at ElectriciansForums.net

.....the contactor is by C&S electrics there an Indian company, there was poor instructions with overload.....
C&S are from the Indian sub continent, I've got first hand experience of there products. Their contactors are okay but I don't like their thermal overloads, I've had more than one that I've bench tested and they've been operating far outside of their published curve.

Here's some info I have immediately available. I've got more on my office server, if I've got time to dig it out tomorrow I will.

View attachment TC Overloads Technical Data.pdf
 
Thanks Marvo, can't access link on tablet, will have to use the laptop.
Can you remember does the auto setting on there overloads need to be pushed in or remain out?
Also is there any other reason to select auto reset other than convenience?
 
do you think the manual reset would be best, does the auto just close the circuit again once the fault has cleared?

Probably, but depends on the circumstances. Auto reset will re-energise the contactor as soon as the overload heaters have cooled down, so if the likely causes of a stalled motor are ones that need manual intervention to correct, then manual reset is much better as the motor will otherwise experience repeated overload conditions until something breaks or someone arrives to sort it. OTOH if the typical cause of an overload is only temporary, such as a compressor trying to restart against backpressure, then auto-reset will get it back in action without a service callout. Single-phase capacitor start motors are vulnerable on auto-reset because the start cap can overheat with repeated prolonged start attempts.

It does sound like the overload relay wasn't responding correctly there, unless the fuse had the wrong wire in or had been weakened in the past.
 
Darkwood it's a 230v coil taped off as you said. Contacts are ok, open and closing on test trip. Just not sure if the auto setting is active when button is in or out.
 
Thanks Lucien, will change to manual reset. Fuse wire was the correct 15a type, think your right that the overload was not active.
Will sort it tomorrow thanks again.
 
It sounds like it's got the wrong overload relay anyway if its lowest setting is 7A and for your motor it should be 6A.


Sent from my iPad using Tapatalk
 
Hi all, motor started tripping again today this time it was the contactor overload. Think it has kicked in now because I have had to lower the overload rating due to the current demand of motor decreasing, think Marvo mentioned last night that this can happen not sure exactly how though.
Could anyone explain why a capacitor motor would decrease in current demand, think the abuse it has taken has done damage just like to know if I can fix it.
 
Head pressure of the pump will have an effect on motor run current. What type of pump is it? Make and model number? What is the pump doing ie what application?
 
Hi Marvo don't have the pump details now, it's used to feed sprinkler system in glasshouses. It has 2.5 to 3 inch pipe coming in from tank actual pump is around 18 inches tall by around 10 inches wide, outgoing pipe is around 2.5 to 3 inches. Think it is a basic pump assembly nothing fancy.
Seen plate on motor today with 9.5a run current, never seen motor draw this much current only 7.5amps then down to 6.
Owner thinks pump is ok, not sure what else could explain current changes in motor though, any idea?
The motor has two caps and two windings, one has a resistance of over 3 ohms the other is over 5ohm, seems ok.
Hope this was of use.
 

Reply to Contactor overload in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

We have this Swiss-made Dixi horizontal borer from 1957, very nice machine still with its original DC variable voltage drive. In those days there...
Replies
9
Views
2K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
I'm looking at a German made roller conveyor system 10 motors contactors controlled by a PLC Issue is customer says 3 mths ago motors started...
Replies
23
Views
3K
Can't seem to figure out the issue on a sump controller I am working on. It is a pre-built controller box, set up for two pumps (lead/lag pump...
Replies
2
Views
2K
Hi all, been asked to go look at a contactor setup on a pump which is only used for garden lawn sprinklers etc.. and as I don't often play with...
Replies
13
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top