H
Hunter3006
Hi guys I am new and struggeling. Can any one pleas tel me why r1+r2 have to be divided by 4 pleas
Discuss Continuity of ring final in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Take a piece of paper, draw what you describe, sit back and think about it.
Hi guys I am new and struggeling. Can any one pleas tel me why r1+r2 have to be divided by 4 pleas
Ruthless Murdoch -- You can draw that, sit back and think about it for hours and still not understanding it!
I agree, and this is precisely what I did last night. I spent a good few hours, and many sheets of paper trying to mathematically prove it was always true, and I couldn't. As I finally nodded off, I realised why:
It's not always true.
The IET are pulling a fast one.
Folks, R1+R2 does NOT always equal (r1+r2)/4.
It does in two situations:
(1) The CSA of your CPC and P are the same (eg 1/1, 2.5/2.5). If this is the case, doesn't matter where around the ring you measure it, R1+R2 always equals (r1+r2)/4.
(2) You measure R1+R2 exactly half way around the ring. If this is the case, doesn't matter what the CSA ratio is (1.5/1, 6/2.5 etc), R1+R2 always equals (r1+r2)/4.
However, if you're using summat like 4/1.5 and you measure at a socket close to the CU, then R1+R2 will be less than (r1+r2)/4.
To illustrate it, I wrote a program in Matlab, and got it to print a graph. Here it is:
View attachment 21401
This shows the ratio of (R1+R1) : (r1+r2)/4, for different testing points around the ring (expressed as "percentage around ring" ie 50% is exactly half way round). The flat black line at the top is the case where the CSA of CPC and P is the same - this is a flat line at height 1, showing that R1+R2 = (r1+r2)/4. All the other coloured lines are for different CSA combinations. Think of your height as "how close to correct" you are: 1 = "spot on", 0.8 = "20% error".
Note that the very lowest number on the height scale, for the cable with the most extreme ratio of CSA, is about 0.8, when your socket is VERY close to the CU.
So although R1+R2 does not stictly always equal (r1+r2)/4:
- for some cases it does (equal CSAs, or half way round the ring), and
- for other cases, it's pretty close.
Every day's a school day
(I appreciate this doesn't answer the OP's question - I can write an explanation for why (roughly) it works if need be... I'm sure others could too if they want to help him out, to be honest I'm pretty kn***ered!)
too much time on your hands. i'd start by typing the first line then give up. :behead:
OK . given you a "like". now can we get back to silly inane posts?
I've given him a 'Thanks'! rrr:
PS "always show your working..."
They get away with by stating it is "approximately 1/4"I agree, and this is precisely what I did last night. I spent a good few hours, and many sheets of paper trying to mathematically prove it was always true, and I couldn't. As I finally nodded off, I realised why:
It's not always true.
The IET are pulling a fast one.
Reply to Continuity of ring final in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net