Discuss Control Panel Star Delta Starter in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

TomS

-
Reaction score
0
Hello all. I’m after a bit of advice. Daft question I’m sure but when wiring a star delta starter in a panel is it necessary to use the electrical interlocks, i.e for the coil of the delta contactor, would you take the wire through the N/C of the Star contactor first?
 
Which is why the uninitiated,can on occasion,open up the panel,and in an effort to "test" or "jog" a troublesome motor,get round to manually poking two contactors at once...and get a fuse time/current demonstration :(
 
Which is why the uninitiated,can on occasion,open up the panel,and in an effort to "test" or "jog" a troublesome motor,get round to manually poking two contactors at once...and get a fuse time/current demonstration :(

Yes coupled with an almighty bang and a flash!
 
Screw up the timing and you'll get an almighty bang.

Had a 300kW HPU starter go "boom" on a job because the time between wye & delta was too short - when the delta came in the wye contactor was still arcing which destroyed both contactors - TWICE before the pre-comm guys figured out the problem along with Schneider.
 
Screw up the timing and you'll get an almighty bang.

Had a 300kW HPU starter go "boom" on a job because the time between wye & delta was too short - when the delta came in the wye contactor was still arcing which destroyed both contactors - TWICE before the pre-comm guys figured out the problem along with Schneider.

Can you expand on that please, it doesn't quite make sense in what you're saying.
 
Wye is the US term for "Star"

Some companies make a "1 size fits all" cubicle. This can be used as master contacter with 2 others contactors which can be programmed via the motor manager unit. These can be programmed as fast / slow, star / delta, heat stage 1, heat stage 2 etc.

The big problem with these was that there were no mechanical interlocks.

Whoever set the starter up had not allowed enough time between star dropping out and delta closing. So when the changeover between star and delta happened the star contactor was still arcing across he contacts at the same time as the delta closed.

Line to line fault on a 300kW, 690V contactor is not a good idea.
 

Reply to Control Panel Star Delta Starter in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi. I need to alter the configuration of this motor wiring from star to delta so that I can use a VFD to control it (hopefully). If I remove the...
Replies
6
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hello, First of all, thank you in advance for any helpful insights posted in response to my question. I have just moved into a new home. With...
Replies
1
Views
1K
Hi there, I got a call to a job, table saw (wood) tripping C/B straight away. 4kW motor on Star Delta Starter. So I get to the job, after some...
Replies
2
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock