Hi there,

Whats the best way to convert a Ring Circuit which feeds all the sockets in the house, to 2 Radial Circuits.

Its an 1960s house so only has one ring circuit. Would like to know the easiest way of doing this without lifting floorboards if possible. Im unsure where the 2 legs of the ring are going from the Dist. Board.

Thanks
 
Do some testing to roughly find the mid point of the ring circuit. Take off a socket and disconnect one of the feeds. Make safe and then connect the two ends in the CU to a couple of 16amp MCB's. Hey presto a couple of radials.
 
Find an appropriate position between two sockets where you want to break the ring then then in an ideal world you would remove the cable that goes between though in the working world you would probably just cut the conductors off right up to the backbox.
Test and inspect the two radials then supply each by a B20 MCB.
 
Do some testing to roughly find the mid point of the ring circuit. Take off a socket and disconnect one of the feeds. Make safe and then connect the two ends in the CU to a couple of 16amp MCB's. Hey presto a couple of radials.

Hum, so in every socket except the one you've now changed you've got 2 cables connected. Me think's you should find the "other end" of the now disconnected cable (i.e. at the next socket/fcu) and disconnect that too. Also you may be able to use 20A MCB's - especially so if one of your "new" radials has a dishwasher and washing machine on it.

Why do you want to split the ring in the first place?
 
Hum, so in every socket except the one you've now changed you've got 2 cables connected. Me think's you should find the "other end" of the now disconnected cable (i.e. at the next socket/fcu) and disconnect that too. Also you may be able to use 20A MCB's - especially so if one of your "new" radials has a dishwasher and washing machine on it.

Why do you want to split the ring in the first place?

Disconnecting the other end of the leg would be better, but makes no difference, you still have two radials, just an extra live cable made safe in one of the back boxes.
 
So you would be happy to leave a live cable from a separate circuit in the back box? Nice when you’ve isolated your radial, tested the socket is dead and then get a belt off the other radial.

I’m baffled why our OP wants to split the ring. (No smutty jokes please).
 
I can't understand why exactly, your splitting this ring?? Is there a fault on the ring that you can't get to or something??

Splitting a ring for no particular reason is just pure folly!! If the property needs another circuit, then fine install one, a Radial if you like. Better still, split the ring and bring a new leg back to the CU from each, to create 2 ring circuits....
 
If, lets say, a RFC had a line of spurs connect into the ring then splitting the ring where multiple spurs had been connected would be a logical solution.
A tree circuit fed from a 20A radial would be a quick solution to having to rewire the whole RFC, don't you think?
 
So you would be happy to leave a live cable from a separate circuit in the back box? Nice when you’ve isolated your radial, tested the socket is dead and then get a belt off the other radial.

I’m baffled why our OP wants to split the ring. (No smutty jokes please).

Ok ok, find the other end, disconnect that too. However, if it is made safe as I suggested, any competent person would check to see whats going on before getting a belt!!!
 
What about an incompetent person? Much better to disconnect both legs. We live in the real world where some people have a little knowledge to make this situation more dangerous than it should be.

Don't seem the point of splitting a ring final unless one part serves an upstairs floor and another "the return" downstairs and you want to be able to isloate either floor for maintenance work.
 
I must admit I would not be happy leaving the cable disconnected at just one end.

There are a few scenarios as to why this is not safe, a couple have already been mentioned.

If you are splitting to separate circuits for a new consumer unit then you'll have to be 100% sure that there are no points on the "Wrong "circuit. I have not seen it personally but I have been informed of installations where the circuit supplying an entire property snaked from one floor to the other in numerous places which would make it near impossible to divide into front/back or up/down.

Regards

1SC
 
I must admit I would not be happy leaving the cable disconnected at just one end.

There are a few scenarios as to why this is not safe, a couple have already been mentioned.

If you are splitting to separate circuits for a new consumer unit then you'll have to be 100% sure that there are no points on the "Wrong "circuit. I have not seen it personally but I have been informed of installations where the circuit supplying an entire property snaked from one floor to the other in numerous places which would make it near impossible to divide into front/back or up/down.

Regards

1SC
It used to be quite a common way to wire the one RFC for the house. Still possible to find the approximate mid point for a split by checking resistances.
 
Still possible to find the approximate mid point for a split by checking resistances.

Oh most definitely, I should have emphasised more. Great care will be required to ensure that all outlets are tested so that the labelling of the consumer unit can be done correctly and in a way that will never put anyone at risk ie Front radial, rear radial or up and down. This could become less straightforward if after finding the mid point there is power on both floors.

:thumbsup
 
As it's a '60s house:
# it's likely the rfc is wired in imperial 7/029 which has a rating of 31A. Watch for modifications though which have been made in 2.5
# it was common to have only one rfc, but several of the sockets may well be spurs, particularly where there are sockets on the same wall with one upstairs and one downstairs. Make sure you know which 'half' each socket is on.

Also, some manufacturers do 25A mcbs (Hager for example), so you may be able to create 25A radials.
 
I notice whazza22 hasn’t come back to explain why he wants to split the ring.

I thing this is a dead horse beyond flogging. :banghead:
 
Last edited by a moderator:

Reply to Convert Ring Circuit to 2 Radial Circuits? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi! Is there any way to know if I have a ring or a radial circuit in a division of the house? Thanks!
Replies
6
Views
2K
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
244
hi all come across a new build commercial office where radial circuits feeding electrak power track was protected by 32A RCBO at dist board and...
Replies
15
Views
1K
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
985
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
699

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock