Discuss Correct Gauge Wire For Parallel Dual Battery in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
First Install with a Parallel circuit or this distance.

Connecting 2x 12V 90ah AGM batteries in parallel and the cable length with roughly be 2 meters in length. Putting the batteries any closer is not an option due to space restrictions. 20-30amps is roughly what will be drawn at one given time in the circuit for the time being.

What size cable/amp is best suited?

Much appreciated
 
Have you tried an online cable sizing calculator ? There are many of them out there... such as this one:

But... remember that with DC, you want the total length of +ve & -ve added together... and... if I were you... treat the result given from the calculator as an absolute minimum... go as big as you can afford/install/manage etc. Also, make sure that you have proper crimped terminal lugs at the end of each cable.
 
I would be working with 25mm trirated or welding cable as a minimum.
It will help avoid volt drop.
But more importantly, 2 batteries of that size in parallel will provide several hundred amps if there was ever a short circuit.
 
Other than the maximum load current to be drawn, the most important criterion for battery cable size is usually what kind of charger is being connected and where, because voltage drop during charging is extremely detrimental to charging performance and could result in one battery receiving less charge than the other. As above, with batteries of that size, although the length is short there's no excuse for using less than say 25mm² / #3 AWG copper. This will ensure that at any charge rate the batteries can handle the voltage drop will not be an issue. It will also probably survive a momentary short-circuit, but fusing at the posts e.g. with the cube fuses mentioned is a very good way to protect against burnout. Additional fusing might be needed to protect the wiring downstream.

remember that with DC, you want the total length of +ve & -ve added together.

Perhaps I've missed the point but I am not sure how that differs from AC other than the names of the conductors.
 

Reply to Correct Gauge Wire For Parallel Dual Battery in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I thought that I posted this in the DIY part of the forum but I believe I did not. I am sorry about that. I put in a 10' x 20' metal shed about...
Replies
2
Views
1K
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Ok so live in 89 mobile home ugh I really need lots of work but I'm on disability and I cannot afford electrician but I've been working with all...
Replies
1
Views
811
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
806
Last year we purchased a home that was built in the late 1990s It has one outbuilding, sort of a barn/shed about 160 feet from the house (and...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock