Discuss Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

You can consult the supplier but as to what you can do about it, very little. I assume this is a TN-S supply where the suggested Ze should not exceed 0.80 but this is not an absolute requirement.
I should correct myself, it is a 32A mcb with an 80A type A rcd fitted at the c/u. Also the box in the field where the 16mm SWA originates appears to show the system as TNCS as SSE have the earth coming out of their service head.
 
The maximum permitted Zs for any final circuit with a 30ma 61009 or 61008 device at its origin is 1667 ohms, so the Zs on your ring circuit is satisfactory on a 32a rcbo.
Hi, isn't the 1667 ohms reading only for Type S RCD's? in page 70 of the regs i see that value in a table. regarding S type?
 
I should correct myself, it is a 32A mcb with an 80A type A rcd fitted at the c/u. Also the box in the field where the 16mm SWA originates appears to show the system as TNCS as SSE have the earth coming out of their service head.
Fault protection is still provided by the RCD.
If it is TN-C-S then the armour of that cable is inadequate to support main protective bonding.
 
Fault protection is still provided by the RCD.
If it is TN-C-S then the armour of that cable is inadequate to support main protective bonding.
Perhaps i should suggest to the farmer an earth spike should be installed at the meter box beside the two cottages in order to provide an adequate earthing arrangement?
This is where the SWA terminates into the box 300 yards away. Don't you think that the cable size is massively underrated for the distance?Mains supply box in field.JPG
 
Last edited by a moderator:
It is certainly undersized by some way but they are not necessarily working to the requirements like us. I would question it and see their response.
 
It is certainly undersized by some way but they are not necessarily working to the requirements like us. I would question it and see their response.
This cable was not run by the electricity supplier. It was run by a previous electrician who did work on the farm and this cable was reconnected into the new mains box when the supplier brought in new overheads. So unfortunately it isn't them who are to blame, but some old retired spark somewhere around here! 😑
 
Got you. That cable is certainly undersized with regard to volt drop which isn't necessarily a concern with an EICR unless it is giving issues but the armour is, personally I Code 2 these instances as it is inadequate to support main protective bonding.
 
Agree with westwood That SWA need terminating correctly. I would give a code 2 for that. I would also code 2 those exposed single insulated cores of the SWA . To fix the HI zs though you would have to down rate the main fuses, fit a main upfront 300ma RCD at the DNOs supply box Or run in a new cable.
 

Reply to Cottage supplied by 16mm SWA 300+ yards! Trying to resolve a high Ze reading in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
915
Hi everyone, i might be having to run new meter tails from meter box to consumer unit which is just under 3m run, i have used 25mm 3 core before...
Replies
6
Views
3K
All of the work described below will be completed by a qualified electrician, I am just curious and using the info for planning!! I am planning a...
Replies
13
Views
4K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock