Discuss Could I ask if you could help explain the comments re a Domestic ElCR report that has come back unsatisfactory please in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
6
Background: I have a ex council 1st floor flat that I bought, I moved in to care for my disabled mum and so rented the flat as I could not do enough hours work and care.

I was told I am a kind landlord and when asked to do things I will jump immediately as I would not like my tenant to have a problem. The tenant was found by an agent who is initially the main point of contact for medical reasons on my part. However, after a bad expereince of a not so good professional suggested by them. I have used my preferred sparky and plumber and I book them to do the certificates and checks and services. However, my lovely sparky retired 2 years ago and is NOT NIC registered anymore.

I was sent a letter back in March stating the new laws means I needed an EICR satisfactory report done on the flat ASAP as I am renting my flat out. (Then COVID hit)

Anyway, I finally booked a company online 'Landlord Certificates' to do the test and today I have received a very technical report 8 pages long with two other booklets with codes in that I am beside myself with worry over and do not understand but they have pointed out a C2 which means danger and said because of that even the C3's must be put right by law.

Please please could anyone help me to explain what these mean as I truly do not fully understand them so I know what the issue is and then what I need to do as in work (of course a Sparky). I would also be grateful for a guide price to as I think I may need to go to get a loan.

On the reports it has 4 items unsatisfactory:

1. 4.11a The consumer unit has no circuits chart - C3 (Consumer Unit)
2. 5.11 C The consumer unit has no RCD for additional protection for cables installed in walls and partition with a depth less than 50mm. - C3 (Consumer Unit)
3. 8.4 Absence of supplementary bonding where required in a location containing a bath or shower, where all final circuits of the location comply with the requirements of Regulation 4.11 3.2 for automatic disconnection and all final circuits of the location have additional protection by means of a 30mA RCD and all extraneous-conductive parts of the loca C2 (Bathroom)
4. The consumer unit is made from combustible material does not comply with the 18th edition of the wiring regulations - C3 (Consumer Unit)

I know my consumer unit is made of the cream coloured plastic.
The bathroom when it was installed 4 years ago, they put 6mm bonding in as I emailed to check with my retired sparky.

He did say the panels can be removed to see pipes, it just needs to be unscrewed and the bath to be careful so they do not crack the panel on the bath. However, he did advise as he is no longer in the game to get advice from a Electrical forum in the first instance as people will explain it in different ways which might make it easier to understand. (He also said to be careful that there are lots doing this 'certificate' and ripping you off, which has of course worried me even more in my situation.

I am beside myself, since renting I have not raised the rent, 4 years, I am the cheapest in my estate but I know that my tenant is a kind man and does a manual job and I did not rent my flat to profit it was so the flat pays for itself as in the mortgage and bills and had a person living in it rather than empty and at risk. However these last two years there has been more and more certificates I am being told must be done yearly which is quite expensive.

To add insult to injury I was told only yesterday I am being laid off and now have that, which looking on here under consumer units, there was a lot of people talking about what they charge and some saying I charge ÂŁ45 per hour because they can afford it and commenting on what people are paid e.g. newspaper boy ÂŁ9.00. Consumer units being ÂŁ200 to buy but charging ÂŁ1,000. I am beside myself honestly.

It is not just young people who struggle to make a living, as a carer we get ÂŁ9.59p per hour and have to do long days, very manual intensive and hard providing care for elderly, vulerable, frail, ill, some beat you black and blue as they do not realise you are trying to help, we do courses and have qualifications for medication/first aid/life saving skills as well as others, I wish the job was appreciated and paid better but sadly it is not and not appreciated and for most until you need a carer for a relative you do not think of them as educated and hard working.

Sorry everyone, you can probably tell I am very emotional and worried and upset by it.
 
Don't be fretting too much, the only thing you need concern yourself with are the C2 items. Anything C3 are recommendations which should not deem the installation unsatisfactory, in other words it would be safe for continued use. Rectifying your C2 issue is no more than an hours work to put in place supplementary bonding. This should remove the need for circuits in the bathroom requiring additional rcd protection.
 
if there is supplementary bondin in the bathroom it's a C3, C3's mean improvement recommended. but still a satisfactory report.

replacement of a consumer unit with RCD protection as required should not cost more than ÂŁ350 (dual RCD board) or up to ÂŁ500 (RCBO board). these figures assuming a board of up to 10 MCBs./RCBOs. and including a Installation Certificae (EIC).

Bet there's a member on here close enough to give you a reasonable quote.
 
There is no bonding in the bathroom, the consumer unit does not need replacing according to the findings.
 
As Westward says, don't fret too much. It doesn't seem as bad as you may think. I bet someone on here would give you a 2nd opinion.
 
Background: I have a ex council 1st floor flat that I bought, I moved in to care for my disabled mum and so rented the flat as I could not do enough hours work and care.

I was told I am a kind landlord and when asked to do things I will jump immediately as I would not like my tenant to have a problem. The tenant was found by an agent who is initially the main point of contact for medical reasons on my part. However, after a bad expereince of a not so good professional suggested by them. I have used my preferred sparky and plumber and I book them to do the certificates and checks and services. However, my lovely sparky retired 2 years ago and is NOT NIC registered anymore.

I was sent a letter back in March stating the new laws means I needed an EICR satisfactory report done on the flat ASAP as I am renting my flat out. (Then COVID hit)

Anyway, I finally booked a company online 'Landlord Certificates' to do the test and today I have received a very technical report 8 pages long with two other booklets with codes in that I am beside myself with worry over and do not understand but they have pointed out a C2 which means danger and said because of that even the C3's must be put right by law.

Please please could anyone help me to explain what these mean as I truly do not fully understand them so I know what the issue is and then what I need to do as in work (of course a Sparky). I would also be grateful for a guide price to as I think I may need to go to get a loan.

On the reports it has 4 items unsatisfactory:

1. 4.11a The consumer unit has no circuits chart - C3 (Consumer Unit)
2. 5.11 C The consumer unit has no RCD for additional protection for cables installed in walls and partition with a depth less than 50mm. - C3 (Consumer Unit)
3. 8.4 Absence of supplementary bonding where required in a location containing a bath or shower, where all final circuits of the location comply with the requirements of Regulation 4.11 3.2 for automatic disconnection and all final circuits of the location have additional protection by means of a 30mA RCD and all extraneous-conductive parts of the loca C2 (Bathroom)
4. The consumer unit is made from combustible material does not comply with the 18th edition of the wiring regulations - C3 (Consumer Unit)

I know my consumer unit is made of the cream coloured plastic.
The bathroom when it was installed 4 years ago, they put 6mm bonding in as I emailed to check with my retired sparky.

He did say the panels can be removed to see pipes, it just needs to be unscrewed and the bath to be careful so they do not crack the panel on the bath. However, he did advise as he is no longer in the game to get advice from a Electrical forum in the first instance as people will explain it in different ways which might make it easier to understand. (He also said to be careful that there are lots doing this 'certificate' and ripping you off, which has of course worried me even more in my situation.

I am beside myself, since renting I have not raised the rent, 4 years, I am the cheapest in my estate but I know that my tenant is a kind man and does a manual job and I did not rent my flat to profit it was so the flat pays for itself as in the mortgage and bills and had a person living in it rather than empty and at risk. However these last two years there has been more and more certificates I am being told must be done yearly which is quite expensive.

To add insult to injury I was told only yesterday I am being laid off and now have that, which looking on here under consumer units, there was a lot of people talking about what they charge and some saying I charge ÂŁ45 per hour because they can afford it and commenting on what people are paid e.g. newspaper boy ÂŁ9.00. Consumer units being ÂŁ200 to buy but charging ÂŁ1,000. I am beside myself honestly.

It is not just young people who struggle to make a living, as a carer we get ÂŁ9.59p per hour and have to do long days, very manual intensive and hard providing care for elderly, vulerable, frail, ill, some beat you black and blue as they do not realise you are trying to help, we do courses and have qualifications for medication/first aid/life saving skills as well as others, I wish the job was appreciated and paid better but sadly it is not and not appreciated and for most until you need a carer for a relative you do not think of them as educated and hard working.

Sorry everyone, you can probably tell I am very emotional and worried and upset by it.
What is your post code Kirstie? if not to far may come and advise only ( to old to take on the work, bad hips bad back etc)





)





if you wish
 
It seems the company has done a very thorough job.... rather than a 2 hour drive by type test. An EICR is 5 pages long, minimum.
But as mentioned above, there is only one thing on there that need actually worked on. The rest, C3's, are still ok, and NOT dangerous.


It may be a chance to raise your rent... just a little to pay for these remedial works. Your tenant will understand, if you're the cheapest around just now.
 
1. 4.11a The consumer unit has no circuits chart - C3 (Consumer Unit)
2. 5.11 C The consumer unit has no RCD for additional protection for cables installed in walls and partition with a depth less than 50mm. - C3 (Consumer Unit)
3. 8.4 Absence of supplementary bonding where required in a location containing a bath or shower, where all final circuits of the location comply with the requirements of Regulation 4.11 3.2 for automatic disconnection and all final circuits of the location have additional protection by means of a 30mA RCD and all extraneous-conductive parts of the loca C2 (Bathroom)
4. The consumer unit is made from combustible material does not comply with the 18th edition of the wiring regulations - C3 (Consumer Unit)
considering its not bad a bit of tweaking all that its needed c2 nobody going to throw a book at you ,get the sparks back and bond that bathroom .
 
What is your post code Kirstie? if not to far may come and advise only ( to old to take on the work, bad hips bad back etc)

if you wish


Dear Pete,

My Flat that has failed is in Waltham Abbey, Essex. I thank you for your offer and kindness. But am initially going to contact the Engineer inspector who did the inspection to see if he is willing to quote to sort the Bathroom bonding out as a lot of the lovely people on here have suggested.

As I know that whoever does the work has to then issue the certificate and do the EICR again so it can be deemed as satisfactory.

From what all you lovely people are saying is that even though the flat has a tenant that I do not legally have to do the C3 work as it is not life threating at the moment it is just rules and ideas have changed and been made into codes.

That is a big weight off of my mind. Thank you for your offer, if however the person does not come back to me I may be back to ask for next step and see if there are any registered sparkies near me. Thank you again.
[automerge]1593621732[/automerge]
Just wanted to say thank you to you all for your replies. It has certatinly put me in a more calmer state.

I take on board your comments and will go back to the person/company who did the inspection to ask for a guide on availability and price to resolve the C2 aspect so that I can have a certificate that says satisfactory and I know my Tenant is safe.

I really appreciate you guidance everyone thank you so much, I honestly thought I was in for a rough road. It does not seem at all that bad now you have explained it to me in language that I can comprehend, Thank you :0)
 
As I know that whoever does the work has to then issue the certificate and do the EICR again so it can be deemed as satisfactory.
No, a minor works certificate to cover the aspect of the C2 would be adequate. Shouldnt need to do the EICR (and charge you) again!

If existing tenant, you do not need to produce an EICR until April next year.

I would certainly get another sparky to quote!
 
3. 8.4 Absence of supplementary bonding where required in a location containing a bath or shower, where all final circuits of the location comply with the requirements of Regulation 4.11 3.2 for automatic disconnection and all final circuits of the location have additional protection by means of a 30mA RCD and all extraneous-conductive parts of the loca C2 (Bathroom)

I'm confused by item 3. Maybe I'm missing something?
If there is additional protection by means of 30ma RCD, and the other requirements are met, then SB is not required.
If there is no additional protection by means of 30ma RCD then why hasn't that been coded? It is a non -compliance regardless of the presence or not of SB.
 
I'm confused by item 3. Maybe I'm missing something?
If there is additional protection by means of 30ma RCD, and the other requirements are met, then SB is not required.
If there is no additional protection by means of 30ma RCD then why hasn't that been coded? it is a non -compliance.
the idea is rcd protection not there covering the bathroom then any thing will require bonding a protentional where mrs gibbons decides to change a bulb or fitting standing in the sink and foot touching the taps . :eek:
 
Dear Pete,

My Flat that has failed is in Waltham Abbey, Essex. I thank you for your offer and kindness. But am initially going to contact the Engineer inspector who did the inspection to see if he is willing to quote to sort the Bathroom bonding out as a lot of the lovely people on here have suggested.

As I know that whoever does the work has to then issue the certificate and do the EICR again so it can be deemed as satisfactory.

From what all you lovely people are saying is that even though the flat has a tenant that I do not legally have to do the C3 work as it is not life threating at the moment it is just rules and ideas have changed and been made into codes.

That is a big weight off of my mind. Thank you for your offer, if however the person does not come back to me I may be back to ask for next step and see if there are any registered sparkies near me. Thank you again.
[automerge]1593621732[/automerge]
Just wanted to say thank you to you all for your replies. It has certatinly put me in a more calmer state.

I take on board your comments and will go back to the person/company who did the inspection to ask for a guide on availability and price to resolve the C2 aspect so that I can have a certificate that says satisfactory and I know my Tenant is safe.

I really appreciate you guidance everyone thank you so much, I honestly thought I was in for a rough road. It does not seem at all that bad now you have explained it to me in language that I can comprehend, Thank you :0)
OK Kirstie thanks, hope you get it sorted.
 
This should remove the need for circuits in the bathroom requiring additional rcd protection.
Just for clarity it won't remove the requirement for them to have additional protection by a 30mA RCD, although it is likely to leave it in a satisfactory condition. (Possible exceptions might be the likes of an electric shower not 30mA RCD protected.)
 
Kirstie, if possible could you post up the report so we can take a look?

It would need to have any names, addresses, company details etc blanked out.

C3 means improvement is recommended but would still result in a satisfactory report if no C2 or C1 conditions exist, therefore these don't technically need sorting. To state they have to be put right by law is nonsense and scaremongering.

C2 means potentially dangerous and will need rectifying.

C1 means danger present and will need rectifying.

The problem with the recent changes is a lot of companies are jumping on the band wagon and quoting ridiculously low prices to carry out testing. They will then give an unsatisfactory report to make money on the remedial works. Morally corrupt.

Even if the inspector rectifies all the faults the report will remain unsatisfactory. Any certificates for the rectification works would then show that the work has been completed, there is no requirement to issue a new report.

In five years time the next inspector would look at old reports and certificates to see what faults were present and if they were rectified. They would also be able to tell if any dangerous conditions have reoccurred through trends, such as shower switches overheating for example. If all they see is satisfactory reports over the years then the installation must be perfect and nothing ever goes wrong.

I would advise speaking to your retired electrician as they must know a trusted trader in your area.
 
the idea is rcd protection not there covering the bathroom then any thing will require bonding a protentional where mrs gibbons decides to change a bulb or fitting standing in the sink and foot touching the taps . :eek:
RCD protection is required to all final circuits in a bathroom, the fact that SB is or is not installed is irrelevant, it still requires additional protection and if that is not present it should have been coded.

If additional protection is present then SB is unlikely to be required.
If additional protection is not present then that should have been coded.

As I read it the report recommends the installation of SB, so presumably additional protection is not present. Even if SB is installed lack of additional protection should still get a code 3, and the report apparently says it is a legal requirement to rectify code 3's!

The correct way to rectify this based on the report recommendations is not to install SB, but to provide additional protection to bathroom final circuits.

Item 3 in the report does not make any sense.
 

Reply to Could I ask if you could help explain the comments re a Domestic ElCR report that has come back unsatisfactory please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
656
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
Hi Everyone, Last year arranged for my mother's and my consumer units to be changed by the same electrician who is NICEIC registered. Both jobs...
Replies
20
Views
2K
Hi Everyone, I had a new consumer unit installed in December 2021, the electrician said that he had more testing to complete and would come back...
Replies
28
Views
3K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
41
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock