Discuss couple of circuits sharing same earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

amlu

-
Esteemed
Reaction score
804
Hi :)
Im finishing rewiring at the moment, place has concrete ground floor, all cables going under the floorboards on first floor or in the loft. There is couple of steel conduits embedded in the building from where consumer unit goes to floor void above. They end up nicely in a metal box where connections can be made (singles in the conduit to twin and earth) Added couple of new circuits and not sure if all will fit in the conduits.
Got 3x 4mm radial, 1x 2.5mm radial and 10mm bonding for water service to squeeze in, to save on space can I run one earth and split it into separate circuits, wonder if thats any good ?
 
Conduits may be usable for earth but they are old and rusty, metal enclosure on the other end does not have any terminals, its just a box, plan is to drop another run of 10mm earth single and terminate it with an earth block...
11082015514.jpg
 
Last edited:
Isn't there a limit in the British regs that limits the percentage you can fill a conduit. Current carrying capacities are usually given for cables in conduits assuming a certain airflow and cooling effect, if the conduit is filled tight with wiring you'd usually need to derate accordingly. This is the case with my local SA regs and withsome of the ISO regs.
 
Isn't there a limit in the British regs that limits the percentage you can fill a conduit. Current carrying capacities are usually given for cables in conduits assuming a certain airflow and cooling effect, if the conduit is filled tight with wiring you'd usually need to derate accordingly. This is the case with my local SA regs and withsome of the ISO regs.
Yes there is, but it's rarely complied with.
 

Reply to couple of circuits sharing same earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
870
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
Correctly closing off a dead twin and earth cable in a loft. My old house used to have radial circuits serving night storage heaters. Those...
Replies
4
Views
2K
Hello all, Just had an electrician wire in a radial circuit in my house to my loft as I use the space for my home theatre equipment & wanted a...
Replies
30
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock