Hello can anyone advise what they would do in this situation please. I have a wylex 100amp switch fuse that has an incoming and out going cpc connection which takes up to a 16 mm cpc. I have 16mm incoming and outgoing cpc, however how do I then earth the enclosure and the banjo as the cpc connection has no connection with the enclosure
 
Could it be fixed physically with one of the box fixing screws, then a 6mm jumper to the box's terminals? Or maybe better just a 10mm jumper to lug on piranha / Earthing nut as quicker than banjo, etc?
I will get over with unnecessary work as the switch fuse by wylex is very poorly designed
Could it be fixed physically with one of the box fixing screws, then a 6mm jumper to the box's terminals? Or maybe better just a 10mm jumper to lug on piranha / Earthing nut as quicker than banjo, etc?
i still think there are a lot of these installed where the installer thinks the cpc connection is common to the enclosure
 
It really is a terrible design putting in such a small separate terminal however Wylex may have calculated the worst scenario for fault protection and that a 6.0 would satisfy. I would email them.
 
They are rubbish considering the price of them, as usual the designer has never had to fit one or they would have noticed the massive cock up with the earth terminal!
The last one of those I fitted I ran the SWA cpc to the earth banjo bolt and lugged the 16mm outgoing on that as well. As stated above an earth nut would probably be quicker!
Sy
 
They are rubbish considering the price of them, as usual the designer has never had to fit one or they would have noticed the massive cock up with the earth terminal!
The last one of those I fitted I ran the SWA cpc to the earth banjo bolt and lugged the 16mm outgoing on that as well. As stated above an earth nut would probably be quicker!
Sy
Yes I agree that’s what I will do thank you
 
Yes I will and I I get a reply I will let you know
I’ve fitted loads of these switch fuses. In fact I will be fitting one on Friday coming.

I ignore the earth terminals with Allen heads. I just use the terminal for on the back of the enclosure which you think only takes 6mm2. Unless they have changed the design in the past couple of months (very much doubt) then this earth bar has space for 3x 16mm2 cables. It may look as though it doesn’t but I’ve done it many times. One incoming earth, one outgoing earth and one to banjo.
 
I’ve fitted loads of these switch fuses. In fact I will be fitting one on Friday coming.

I ignore the earth terminals with Allen heads. I just use the terminal for on the back of the enclosure which you think only takes 6mm2. Unless they have changed the design in the past couple of months (very much doubt) then this earth bar has space for 3x 16mm2 cables. It may look as though it doesn’t but I’ve done it many times. One incoming earth, one outgoing earth and one to banjo.
I asked in #13 If a 16.0 would fit.
 
I’ve fitted loads of these switch fuses. In fact I will be fitting one on Friday coming.

I ignore the earth terminals with Allen heads. I just use the terminal for on the back of the enclosure which you think only takes 6mm2. Unless they have changed the design in the past couple of months (very much doubt) then this earth bar has space for 3x 16mm2 cables. It may look as though it doesn’t but I’ve done it many times. One incoming earth, one outgoing earth and one to banjo.
Hi Matt I really didn’t think you could get 16mm in that little earth block
 
Put a separate 6.0 in. I would personally email them they have taken a real step backward from the previous design.
I've always rated Wylex as decent and solid but they've taken a few backward steps, IMO. That looks a bit of a mess all round. As someone said, go back to the old method and link everything via chassis bolt.
With their latest CU's the whole internal unit is no longer fully removal from the chassis making things awkward with replacement units.
 
The Wylex brochure shows a picture of the small 3 way earth bar and the caption says 16mm earth terminals.
Hi wylex replied to me today with this solution
68B4F9D1-D3CC-4376-BCEF-8730F78574F1.png
 
Last edited by a moderator:
That is unbelievable! Wylex used to be good quality gear, having said that most of the big names seem to be going the same way these days!
I am not a fan of adding needless extra connections as it just adds more potential failure points!
I would still be crimping onto a banjo or earth nut imho!
Sy
 

Reply to Cpc connection wylex in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top