Have you used ferrules on your RCBO fly leads?
Looks like the SWA is a 4 or 5 core.Looks neat,not sure of the actual workings of the system.
Where’s the bottom main switch fed from.
Yes that is true the bottom main switch is for the off peak supply feeding storage heater and immersionLooks like the SWA is a 4 or 5 core.
No none of the boards have ferrules I understand that is a requirement but my foreman will not listen.Does look good, be prepared to be ripped apart though
Have you used ferrules on your RCBO fly leads?
We are installing 200 of these board in a council estate. The cables on the left are being boarded .only thing i can fault is the bunch of cables coming in top left.some vertical plastic trunking would look better. otherwise a very neat job.
Thanks for your reply I agree with what you are saying. I have previously uploaded a past board from this job and received the same feedback. My foreman is refusing to purchase ferrules does not think they are needed.If the flylead is fine-stranded and has been cut and terminated in a terminal that is not designed for fine-stranded cable, then that is a genuine defect in the work. Bring your own ferrules or leave the full length of the flylead so you can terminate using the original crimped / spotwelded end.
I'm presuming you only need to add ferrules if you shorten the lead, or do you guys add them anyway?
show him reg. 526.9. ( from 17th . 18th. may be different number.).