Discuss Critical feedback request - Consumer unit. in the UK Electrical Forum area at ElectriciansForums.net

Good on you for asking :) .
Re the bottom row - out of habit I put the isolator on the end. As you've shortened the RCBO N lead, these can't easily be moved now. And yes, if you are going to shorten that N lead it needs to be ferruled. If there's room (seems plenty here) I would use the RCBO as they're supplied.
 
Nice looking job, good to see when someone takes pride in the end result. Agree with all the other comments and will add; don't forget to fill those gaping cable entry holes (the top one's going to be a bitch) with intumescent seal or equivalent fire stop especially as the unit is mounted on a wooden backboard.
 
Can't be arsed with arguing, but where does that **** come from? :)

17th Edition Amendment 3, 421.1.201 (ii)
states that consumer units shall be enclosed ...etc.

You can hardly call the CU enclosed if there's a gapping big hole in the back, especially as it's pointing at an easily combustable material such as wood.

The intent of that reg is to ensure the fire containment of the enclosure is maintained, which it isn't with a big hole in the back facing wood. It would be fine if it was mounted on a non-combustable wall, but it's not.

Think about it, what's the point of having metal enclosures, metal self closing doors over the mcbs, having to fit non combustable blanks, all designed to keep a fire within the CU, then a big hole that a fire can escape out the back of?

A couple of intumescent pillows stuffed in the holes will suffice.
 
17th Edition Amendment 3, 421.1.201 (ii)
states that consumer units shall be enclosed ...etc.

You can hardly call the CU enclosed if there's a gapping big hole in the back, especially as it's pointing at an easily combustable material such as wood.

The intent of that reg is to ensure the fire containment of the enclosure is maintained, which it isn't with a big hole in the back facing wood. It would be fine if it was mounted on a non-combustable wall, but it's not.

Think about it, what's the point of having metal enclosures, metal self closing doors over the mcbs, having to fit non combustable blanks, all designed to keep a fire within the CU, then a big hole that a fire can escape out the back of?

A couple of intumescent pillows stuffed in the holes will suffice.

I'm freshly back. :)

Reg 421.1.201, item (ii) refers to using a enclosure made from combustible material to be installed in a cabinet or enclosure made from non combustible material, i.e. comply with (i) or (ii).

MythBreakers videos - https://www.hager.co.uk/news-exhibitions-case-studies/news/amendment-3-to-bs-7671-2008/mythbreakers/56067.htm?mainvideoid=6dnZNI0bzRk

Unless they have changed the reg again in the 18th (I only have the BYB), there is no requirement to use intumescent seals in a CU made from non combustible material, only to maintain the IP ratings as per reg 416.2.1 (BYB). I don't believe the back of a CU requires this rating, although if someone could access the back, it would make common sense to maintain a similar IP rating.
 

Reply to Critical feedback request - Consumer unit. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good morning guys Was looking for advice with regards to installing an outdoor consumer unit. Customer is looking for power to be installed from...
Replies
9
Views
237
hello all...whats the typical cost for a new consumer unit fitted and the old wired fuse box removed im in a semi detached house in...
Replies
2
Views
267
Hi all I am after some advice on an installation I have coming up. Its a new TP+N circuit in SWA (13m run clipped direct) for a 22kW Tesla wall...
Replies
0
Views
84
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi. Can a horizontal 200A consumer unit be fitted vertically, or is there a vertical configuration? I have a 350mm wide space...thanks.
Replies
19
Views
876

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock