Discuss CU Cable Bunching..? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

jon557

-
Reaction score
0
Hi,

Quick question that has been baffling me, I have seen many CUs whereby the cables enter shared entry points. Does this not mean the cables are now bunched according to the regs? And this all cables should have been calculated with the capacity drop? Or is a CU entry just a bit pedantic for that?

The Victorian house I am working on at the moment has all the cables coming through one hole in the ceiling to the CU also, so I guess the same issue there. I have made separate holes for my work though.

Just wondered what people do about this. I read a lot on this forum about regs but also common sense - as if you can't always follow all the regs to the letter because sometimes you have to make a safe and common sense judgement call on a unique installation.

Cheers.
 
Not all circuits require a grouping factor to be applied.
Circuits/cable grouping factors are based on the assumption that all cables in a group are carrying rated current. If a cable is expected to carry no more than 30% of its grouped rated current, it can be ignored when calculating the group rating factor.
It’s more for fully loaded cables/circuits.
Cables spaced at twice their diameter away can also be ignored.
See appendix 4 for more details

Put it this way, I rarely install 4mm ring final circuits and 1.5mm lighting circuits in domestic installations based on grouping.
 
Last edited:
Great thanks guys. I asked a STROMA assessor about this too and he said it was fine, the regs are more concerned with bunching cables in a run. I wish the regs would put some extra detail around stuff like this. I follow a few sparks on Youtube, Thomas Nagy is my favourite.

I just checked and I have seen a few of SparkyNinja's videos, one about making CU's look neat - basically saying don't cable tie within the CU, space them if possible. Makes sense. :)
 

Reply to CU Cable Bunching..? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Hi, I'm looking for a bit of advice on a volt drop query we have in our office. I'll explain the scenario and I would really appreciate any...
Replies
3
Views
634
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
804
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
751
Good evening all, I’m currently part way through my apprenticeship and we are working on IB, IN, IZ and IT and volt drop today. And it got me...
Replies
4
Views
430

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock