I am happy with calculating current carrying capacity for straight runs of cable. I am not to sure how the imact of a ring effects the cable calcs? Its hard to see what the possible loads might be. As of this do you take the center point and use maximum demand?

So for example on a 35 meter ring with say 8 sockets on a load of 5kW (21.7A) would you assume socket 4 (assuming half way) is the maximum demand point? or am I way off here?

Cheers
 
best way to think of a ring is if it was one cable, the basic point of it is that the farthest point is half the distance and you are using twice as much cable to get there is its up to 4X better than just the one cable going the hole way... so yes the mid point would be the highest resistance
 
if you are doing a r1 + r2 test then yes, because it is a big figure of eight from of the way you should join the ends up but. doing a loop test under normal load conditions a socket that might be right under the consumer unit for example is going to have a better reading than the one that is on the opposite side of the house. so guess it just comes down to witch ever way you do it. (Zs = Ze+ r1+r2)
 
So what is the current carrying capacity of a 2.5mm[SUP]2[/SUP] ring?

For all other circuits we know the current carrying capacity of the cable so we use the appropriate MCB to protect the cable. Why do we use a 32A MCB for a ring, this means the conductors must be able to handle more than 32A, but how do we know this? The regs have a nice set of tables for all other size conductors but not for a ring.
 
Whenever we design a ring, the conductors should have a minimum CCC of 20A.
This would technically give us a CCC of 40A at the point in the middle of the ring.
The 40A is split between the two conductors 20A on one leg and 20A on the other.
However, at a point a quarter of the way around the ring, ¾ of the current will be on the short leg and ¼ of the current on the long leg.
Which would mean 10A on the short leg and 30A on the long.
BS1363 double socket-outlets are rated at 20A (although some manufacturers' rate theirs higher), so we should only have a maximum of 20A at each socket-outlet.
That's 10A on each leg in the middle of the ring, and 5A and 15A at a quarter way round the ring.
Obviously the closer the first socket-outlet is to the start of the ring, the greater the current that will be on the short leg.
30A (now 32A) was chosen, because it's halfway between 20A the CCC of each cable and 40A the combined CCC of the two cables
 
no, spin is correct. assume for easy maths, that a socket close to the CU has a resistance on the short leg of 1 ohm and on the long leg of 4 ohms. assume the load on that socket is 20A. the current in the short leg will be 16A and the long leg 4A.
 
Kirchoff's current law:
At any node in an electrical circuit, the sum of currents flowing into that node is equal to the sum of currents flowing out of that node.

or his voltage law....
"The sum of the potential differences around any closed network is zero"

still not sure what that has to do with your earlier statement though :lol:

 

Reply to Current carrying capacity of ring circuit in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, go easy on me please, I've just returned to the trade, well I am about to, I received my Gold Card last Thursday. I've been gen'ing up for a...
Replies
4
Views
886
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
806
I have a 37KW motor and need to replace some burnt out 35mm2 tri rated cable(loose connection). I’ve looked at 25mm2 Tri rated cable the data...
Replies
6
Views
3K
Hello, I am a trainee electrician just starting to get into doing cable calculations. I understand them when it comes to a radial circuit but get...
Replies
5
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock