Discuss Current demand & load per phase Q in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
4
Hi all,

This is my first post on this forum. I'm currently doing my C&G 2365 and I've found myself completely stumped on a problem that's probably quite simple, but which I've had a lot of conflicting answers for from various people, which has left me a little confused.

I'm working on a design assignment and I'm calculating my maximum demand for a sub-board and distributing it across phases so that I can select a fuse and an armored cable to feed it from the main board. Two of my circuits on the sub-board are 3-phase.

Anyway, the thing that had me stumped was this. One of my three phase loads is described as "pool & sauna equipment that requires a 32A 400V 3-phase and neutral supply."

A classmate of mine has told me that this means 32A per phase, whereas someone I know in the industry has read it as meaning 32A across phases.

From what I understand, from a star-wound configuration IL=IP, so there is 32A in each phase and this does not change between lines (only voltage). So in my head, they're both correct. However, my classmate has tripled this value to add to his demand (a figure later to be divided into three phases) to a a big old 96A. Others that have chimed in have divided 32A into 3 to get 10.66A. I'm assuming that the rule IL=IP still applies even though the feed is technically not coming from a star-wound transformer, so wouldn't both these approaches be incorrect? Shouldn't we just be adding the 32A to max demand and be done with it?

I really appreciate any clarification I can get on this.

Happy Saturday!
 
Can it be both? Ambiguous and a heap of ----, in all: an ambiguous heap of ----? I will accept that my question is also the same, given that I've been linked to a calculator (which to be fair is still useful, thanks).
 
Let me rephrase my question.

If I was to assume 100% demand on a 32A 3-phase power circuit, would I add 32A to my max demand or would I multiply the 32A per phase to get 96A to add to my max demand?

My guess is the former.

Honest (stupid/ignorant) question.
 
You are over thinking this. The pool requires a 32A triple pole supply, that is 32A per phase. The maximum demand cannot exceed 32A per phase and yes you could take 96A in total if each phase supplied 32A single phase loads but it is distributed across the three phases. For example you could have three 32A single phase sockets one on each phase at full load equates to 96A but each phase is only loaded to 32A.
 
When describing a supply, load, or circuit rating, the current stated is always taken to mean the line current regardless of the number of conductors or phases. As per Westward, about the only situation in which one would take an interest in IL x 3 is when specifying the total rating of single-phase loads that can be served by a 3-phase supply.
 
Let me rephrase my question.

If I was to assume 100% demand on a 32A 3-phase power circuit, would I add 32A to my max demand or would I multiply the 32A per phase to get 96A to add to my max demand?

My guess is the former.

Honest (stupid/ignorant) question.

If you are trying a to add up all of the single phase loads and divide by 3 to get max demand then yes you would have to use 96A for this circuit.
 

Reply to Current demand & load per phase Q in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
985
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
276
Hi All, From what I understand, working out the design current - Ib for single phase is quite easy (max appliance power/voltage). For three...
Replies
7
Views
1K
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Replies
9
Views
1K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock