Discuss d type breakers needing a low zs in the UK Electrical Forum area at ElectriciansForums.net

J

Jake1579

im a 1st year apprentice thats why im asking this question, from what ive gathered the higher the current it takes to trip as in 10 times the rated current etc... for that you need a lower zs than if it was a b type why is that?

my thoughts on it is that becuase you have a higher current so youll need to keep the impedance low so that it can trip the protective device in that desired time but i thought the higher the current the resitance is lower ohms law so i dont really get it.
 
If you have a look at the time/current graphs for OCPD's in the BYB you will be able to see the relationship between current and the time it takes each type of OCPD to operate.You will find a much higher current is required to operate a type D mcb than a type B of the same rating for a 0.4s disconnection time. For a higher current to flow a lower resistance is required,simple ohms law....thus a lower maximum Zs is specified.
 
If I could have a quid for the number of times I have come across circuits that have Zs readings that were too high purely because C type mcb's have been swapped out for D's.
And the reason is usually down to start up currents tripping the latter.
In the scheme of things its not or ever will be the answer to badly designed circuits, but still the practice persists.
 
If I could have a quid for the number of times I have come across circuits that have Zs readings that were too high purely because C type mcb's have been swapped out for D's.
And the reason is usually down to start up currents tripping the latter.
In the scheme of things its not or ever will be the answer to badly designed circuits, but still the practice persists.

It is obviously bad practice to end up with a circuit which will not meet disconnection times. However it is sometimes the case that the use of an existing circuit changes from the original design which necessitates changing the type of mcb. Of course if that is the case then zs must be checked,but it may be that the zs only slightly exceeds the max for the device and that an RCD can take care of disconnection times.
Personally I see that as a practical solution to avoid an expensive rewiring of an otherwise perfectly sound circuit just because the zs exceeds the maximum for a type D or C by a fraction of an ohm.
 

Reply to d type breakers needing a low zs in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m probably going to look stupid here, but it will be worth it if I get the answer 😆, as I can’t fathom it out. I’ve never really thought of it...
Replies
22
Views
715
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi , Currently doing a design project in college and I need to pick a circuit breaker ( In device rating and type) for a food holding equipment...
Replies
17
Views
3K
Hi everyone Recently I have come across an advert of someone selling Afdds C type and the person mentioned the need to sell because Zs was too...
Replies
16
Views
3K
A friend of mine asked me to look at here PV system as she is not getting any power (and thus money) from it. First real issue is the Aurora...
Replies
8
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock