Discuss Damaged 415v 5 pin socket needs replacing for RCD type. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
3
I’m replacing a damaged 415v 5pin socket in an engineering shop which is been used for welding, this will need to be replaced with RCD socket to keep up with the regs. but my question is will the welder trip the RCD.
 
Refer to manufacturers instructions, write risk assessment if necessary. However...... why don't you just wire the thing into an isolator instead??
 
Refer to manufacturers instructions, write risk assessment if necessary. However...... why don't you just wire the thing into an isolator instead??
Sorry I wasn’t clear, In total there are 9 I have to replace which can’t be hard wired because they have to be unplugged and taken away periodically for maintainance purposes etc.
 
If replacing like for like accessories, there is no particular need to bring it up to current standards.
Having said that, RCD protection is deemed necessary for any new sockets installed, not exceeding 32 amps. The option for omitting RCDs with a properly conducted risk assessment is included as a last resort, and should document why it is considered that the risk of harm is lower than you would normally expect in the situation the sockets are installed in. Not the reasons why it is not convenient to install RCDs.
There is no reason why any machine should trip an RCD, but as suggested, check with the manufacturer if in doubt.
 
If replacing like for like accessories, there is no particular need to bring it up to current standards.
Having said that, RCD protection is deemed necessary for any new sockets installed, not exceeding 32 amps. The option for omitting RCDs with a properly conducted risk assessment is included as a last resort, and should document why it is considered that the risk of harm is lower than you would normally expect in the situation the sockets are installed in. Not the reasons why it is not convenient to install RCDs.
There is no reason why any machine should trip an RCD, but as suggested, check with the manufacturer
I agree, but going forward I believe it’s good practice to bring it up to current standards, but yes I’ll definitely check the manufactures.
Thanks
 
For something like a welder then fitting combined RCD/sockets is a better bet than modifying the DB as often the DB will be locked so if an RCD trips it is far less inconvenient to reset the accessible one at a socket.
 
For something like a welder then fitting combined RCD/sockets is a better bet than modifying the DB as often the DB will be locked so if an RCD trips it is far less inconvenient to reset the accessible one at a socket.
Usually the best option anyway with 3 phase. Those RCD add on modules for 3 ph mcbs are expensive and take up a lot of ways in the db.
 

Reply to Damaged 415v 5 pin socket needs replacing for RCD type. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
768
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
795
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
915
Hi, I seem to have an RCD that keeps cutting the power at random times without actually tripping, if I reset it, the power comes on and will stay...
Replies
7
Views
453

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock