If changing the Cu and you complete a zs test on say a radial circuit that you have connected into the Cu, it turns out that there is no cpc present at the point of test, surely it can’t be suggested that you just connect the circuit anyway and leave a comment on the EIC?
The comments box is for non compliance’s to be noted that do not give rise to potential danger and immediate danger.
 
Regs wise I think you are correct teletrix. You shouldn't leave an installation with a potentially dangerous situation after a cu change,

however I think Essex is also correct. I cannot force people to get work done they don't want or cannot afford done.

At the end of the day a new up to date residual current protected board is going to make the whole installation safer under fault conditions that it was before. So in court you can explain that to a judge if nessissary and show your notes on the eir (comments on existing installation).
The potentially dangerous situation is going to be there if you do the work or don't. You haven't made it worst, in fact you've made it safer and made the customer aware.
 
If changing the Cu and you complete a zs test on say a radial circuit that you have connected into the Cu, it turns out that there is no cpc present at the point of test, surely it can’t be suggested that you just connect the circuit anyway and leave a comment on the EIC?
The comments box is for non compliance’s to be noted that do not give rise to potential danger and immediate danger.

There are two boxes. One for non-conformances and one for comments on the existing installation.
 
There are two boxes. One for non-conformances and one for comments on the existing installation.
No, one is for comments on the existing installation and one is for departures which if you as the installer have departed from bs7671 then you must record this on the EIC
 
Going back to the debate
A departure needs to comply with regulations 120.3 , 133.1.3 and 133.5 where as comments on the existing installation in the case of additions or alterations are regulation 644.1.2 ( 18th BBB)
Two completely different things.
Note 644.1.2 says any defect that is revealed during inspection and testing shall be corrected before the certificate is issue during alterations and additions
 
Going back to the debate
A departure needs to comply with regulations 120.3 , 133.1.3 and 133.5 where as comments on the existing installation in the case of additions or alterations are regulation 644.1.2 ( 18th BBB)
Two completely different things.
Note 644.1.2 says any defect that is revealed during inspection and testing shall be corrected before the certificate is issued after alterations or additional works and considering a Cu change is an alteration that requires certification, then it would fall into this regulation
See regulation 644 in general
 
Last edited:
You have followed the Regs. The distribution board replacement is what you have done. You aren't responsible for the entire installation.

I was meaning 132.16
No alteration shall be carried out unless it has been ascertained that the rating and condition of any existing equipment will be adequate for the altered circumstances.

I take existing equipment to encompass final circuits and their condition in relation to safety. I wouldn't ignore the other part of that reg (not quoted) regarding earthing and bonding on a DB change so don't see that I can ignore the quoted part.


I also take note of the EAWR....

Regulation 4
(1) All systems shall at all times be of such construction as to prevent, so far as is reasonably practicable, danger.
(2) As may be necessary to prevent danger, all systems shall be maintained so as to prevent, so far as is reasonably practicable, such danger.
 
Note 644.1.2 says any defect that is revealed during inspection and testing shall be corrected before the certificate is issue during alterations and additions
Your certificate does not cover the existing installation, however. Your certificate should very clearly state that it is in respect of the replacement of the distribution board only. Disconnection times obviously need to be verified as part of this (i.e. Zs testing) - this doesn't mean that you have to tear apart existing circuits.

I've found circuits with the sheath not entering enclosures - therefore basic insulation is exposed. This is clearly a C2 defect, however it does not justify me refusing to re-energise the circuit. I simply need to make them aware of the issues, and what they do then is their own business. Obviously if there were exposed live parts or an immediate fire risk (i.e. a C1 issue) then I would not energise it in the interests of safety without addressing that (at least with a sticking plaster).
 
Your certificate does not cover the existing installation, however. Your certificate should very clearly state that it is in respect of the replacement of the distribution board only. Disconnection times obviously need to be verified as part of this (i.e. Zs testing) - this doesn't mean that you have to tear apart existing circuits.

I've found circuits with the sheath not entering enclosures - therefore basic insulation is exposed. This is clearly a C2 defect, however it does not justify me refusing to re-energise the circuit. I simply need to make them aware of the issues, and what they do then is their own business. Obviously if there were exposed live parts or an immediate fire risk (i.e. a C1 issue) then I would not energise it in the interests of safety without addressing that (at least with a sticking plaster).
I stand by what I said.
If I did a pre test on say a water heater circuit and found that the cpc was not present due to say a breakage then I would not be energising that circuit
 

Reply to Dangerous conditions found during CU change. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi guys, I've gotten AI to write up a terms and conditions for my company and then went through it with AI and tweaked it to make it sound a...
Replies
3
Views
368
Did my first consumer unit change yesterday. A few dodgy things with the old board as I’m sure most will see. Owner wanted bringing up to date...
Replies
54
Views
5K
Hi. This is a gloriously messy installation I looked at this morning at a house a friend just purchased. It t became quickly clear it was more...
Replies
7
Views
1K
Hi. I thought I would introduce myself on here in the hope to gain some valuable information on setting out on my own. I'm 42 and have been an...
Replies
116
Views
10K
I know how I was taught to test a RCD, 6 tests in all two no go, two under 300 mS and 2 under 40 mS with no load. But thinking about it not so...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock