Currently reading:
DB change

Discuss DB change in the UK Electrical Forum area at ElectriciansForums.net

P

Plonker 3

Got a DB change to carry out in a house. 60/80 amp incomer, PME supply. Mains tails buried in walls but are double insulated. Main earth 6mm and bonding in 6mm.

The tails look in good condition. So don't want to change them as they are buried in the wall and cause unnecessary mess, but I think I need to change the 6mm main earth, but not the bonding would this be correct or am I being a bit thick in this thinking?

Took a quick Zs at the db when surveying and it was 0.14 ohms
 

Reply to DB change in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top