Search the forum,

Discuss DB2 (TT) trips DB1 TN-C-S in the UK Electrical Forum area at ElectriciansForums.net

Thinking about it, in the summer I connected power to a DB in a brick built shed (about 5 metres from main house. Customer supplied all materials and I had to take the power source from an existing outside socket (customers preference). 3 core SWA provided so armour and copper core all earthed back to same (PME) earth point. No problem with that from my point of view but when supplying out buildings from which a person is stepping in, and out, potentially hanging on to something live, then my preferred, and standard procedure, is two core (cheaper) SWA, TT earth, and 30mA RCD fed from non-RCD MCB.

Haha, ...Classic!!
 
Thinking about it, in the summer I connected power to a DB in a brick built shed (about 5 metres from main house. Customer supplied all materials and I had to take the power source from an existing outside socket (customers preference). 3 core SWA provided so armour and copper core all earthed back to same (PME) earth point. No problem with that from my point of view but when supplying out buildings from which a person is stepping in, and out, potentially hanging on to something live, then my preferred, and standard procedure, is two core (cheaper) SWA, TT earth, and 30mA RCD fed from non-RCD MCB.

The only thing I insisted on adding was an FCU before the outside socket. I have ever since been surprised not to have received a call saying power to the shed had failed.
 
Ah, we have a clever bugger do we, ...it's a shame you're not as clever in you're role as an electrical tradesman, or in the care shown towards your'e customers. Seems it's all their fault, once you walk away from the job!!
 
Thinking about it, in the summer I connected power to a DB in a brick built shed (about 5 metres from main house. Customer supplied all materials and I had to take the power source from an existing outside socket (customers preference). 3 core SWA provided so armour and copper core all earthed back to same (PME) earth point. No problem with that from my point of view but when supplying out buildings from which a person is stepping in, and out, potentially hanging on to something live, then my preferred, and standard procedure, is two core (cheaper) SWA, TT earth, and 30mA RCD fed from non-RCD MCB.


I think my point would be that providing as good an earth as possible is your primary protective measure, and for some reason you would not make use of a super low Ze available to you.

RCDs are unreliable, and do fail, but more importantly, they are supplementary. Not primary means.

especially if there is a wonderful earth available to use.....?

What am I missing?
 
I think my point would be that providing as good an earth as possible is your primary protective measure, and for some reason you would not make use of a super low Ze available to you.

RCDs are unreliable, and do fail, but more importantly, they are supplementary. Not primary means.

especially
if there is a wonderful earth available to use.....?

What am I missing?


not `especially` if theres a wonderful earth to use it is Sparty..

the earthing arrangements dictate whether a 30mA RCD is for additional..or fault protection

so theres no `especially` about it really..is there:wink:
 
not `especially` if theres a wonderful earth to use it is Sparty..

the earthing arrangements dictate whether a 30mA RCD is for additional..or fault protection

so theres no `especially` about it really..is there:wink:

Think he means when used within a TN system rather than a TT system, where in most cases in the UK, folk seem to be happy bunging in a short twig with 100 to 200 ohm Ra values...
 

Reply to DB2 (TT) trips DB1 TN-C-S in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock