Search the forum,

Discuss DB2 (TT) trips DB1 TN-C-S in the UK Electrical Forum area at ElectriciansForums.net

Why? Because although at 30m it is far enough away from the house and (probably) any extraneous metal, with a TT I have a separate earthing system which is, if you like, under known control conditions and not subject to problems at the suppliers end. TT'ing I agree is not really an issue where step-voltages are highly unlikely but I generally will always TT an outbuilding combined with 30mA RCD.

Sorry, above should say "Exporting PME....."


But you have installed a 10mm 3c SWA so the third core is of sufficient CSA to double as a cpc and main bonding!!
Question--If you were installing external lighting not attatched to the main house but fed from it would you treat the lights as 'outbuildings' and TT them or use the house earthing system?


Edit....To be fair you have not stated the PME cant be 'exported'....but that you prefer not to.I'd have to disagree but thats your choice.
 
Last edited by a moderator:
Why? Because although at 30m it is far enough away from the house and (probably) any extraneous metal, with a TT I have a separate earthing system which is, if you like, under known control conditions and not subject to problems at the suppliers end. TT'ing I agree is not really an issue where step-voltages are highly unlikely but I generally will always TT an outbuilding combined with 30mA RCD.

You may as well TT the house using that argument.
 
In other words Sod the customer you've taken money from!! Magic!!
Any electrician that's fool enough to ditch a perfectly good TN Earth in favour of anything like the totally unreliable recommendations of BS 7671 regarding TT systems, needs Certifying!!

TT or PME, it complies with BS7671 and it is up to him as the installer. Sometimes TT is preferable over PME is bonding is required at sub main. I do either dependant on situation. It is not a case of one size fits all.
 
Thinking about it, in the summer I connected power to a DB in a brick built shed (about 5 metres from main house. Customer supplied all materials and I had to take the power source from an existing outside socket (customers preference). 3 core SWA provided so armour and copper core all earthed back to same (PME) earth point. No problem with that from my point of view but when supplying out buildings from which a person is stepping in, and out, potentially hanging on to something live, then my preferred, and standard procedure, is two core (cheaper) SWA, TT earth, and 30mA RCD fed from non-RCD MCB.
 
TT or PME, it complies with BS7671 and it is up to him as the installer. Sometimes TT is preferable over PME is bonding is required at sub main. I do either dependant on situation. It is not a case of one size fits all.


Very true, but if you read his posts here again, ....Not for this guy!!
 
Thinking about it, in the summer I connected power to a DB in a brick built shed (about 5 metres from main house. Customer supplied all materials and I had to take the power source from an existing outside socket (customers preference). 3 core SWA provided so armour and copper core all earthed back to same (PME) earth point. No problem with that from my point of view but when supplying out buildings from which a person is stepping in, and out, potentially hanging on to something live, then my preferred, and standard procedure, is two core (cheaper) SWA, TT earth, and 30mA RCD fed from non-RCD MCB.

Haha, ...Classic!!
 
Thinking about it, in the summer I connected power to a DB in a brick built shed (about 5 metres from main house. Customer supplied all materials and I had to take the power source from an existing outside socket (customers preference). 3 core SWA provided so armour and copper core all earthed back to same (PME) earth point. No problem with that from my point of view but when supplying out buildings from which a person is stepping in, and out, potentially hanging on to something live, then my preferred, and standard procedure, is two core (cheaper) SWA, TT earth, and 30mA RCD fed from non-RCD MCB.

The only thing I insisted on adding was an FCU before the outside socket. I have ever since been surprised not to have received a call saying power to the shed had failed.
 
Ah, we have a clever bugger do we, ...it's a shame you're not as clever in you're role as an electrical tradesman, or in the care shown towards your'e customers. Seems it's all their fault, once you walk away from the job!!
 
Thinking about it, in the summer I connected power to a DB in a brick built shed (about 5 metres from main house. Customer supplied all materials and I had to take the power source from an existing outside socket (customers preference). 3 core SWA provided so armour and copper core all earthed back to same (PME) earth point. No problem with that from my point of view but when supplying out buildings from which a person is stepping in, and out, potentially hanging on to something live, then my preferred, and standard procedure, is two core (cheaper) SWA, TT earth, and 30mA RCD fed from non-RCD MCB.


I think my point would be that providing as good an earth as possible is your primary protective measure, and for some reason you would not make use of a super low Ze available to you.

RCDs are unreliable, and do fail, but more importantly, they are supplementary. Not primary means.

especially if there is a wonderful earth available to use.....?

What am I missing?
 
I think my point would be that providing as good an earth as possible is your primary protective measure, and for some reason you would not make use of a super low Ze available to you.

RCDs are unreliable, and do fail, but more importantly, they are supplementary. Not primary means.

especially
if there is a wonderful earth available to use.....?

What am I missing?


not `especially` if theres a wonderful earth to use it is Sparty..

the earthing arrangements dictate whether a 30mA RCD is for additional..or fault protection

so theres no `especially` about it really..is there:wink:
 
not `especially` if theres a wonderful earth to use it is Sparty..

the earthing arrangements dictate whether a 30mA RCD is for additional..or fault protection

so theres no `especially` about it really..is there:wink:

Think he means when used within a TN system rather than a TT system, where in most cases in the UK, folk seem to be happy bunging in a short twig with 100 to 200 ohm Ra values...
 

Reply to DB2 (TT) trips DB1 TN-C-S in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon all, Got a bit of a strange one (by my usual standards anyway). Job is a large barn conversion, done years ago, there's loads of work to...
Replies
6
Views
1K
Trying to understand why car chargers attract this earthing ballache. from what I learnt it's all about the rare times a Neutral / PEN conductor...
Replies
6
Views
2K
Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
983
The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top