Hello mainline, I looked at the contactor/relay that was for the 3phase it has a 24vac coil.You don't need a DC relay, for instance a 24v 2 pole contactor would be better using a simple 24v transformer.
Hello mainline, I looked at the contactor/relay that was for the 3phase it has a 24vac coil.
Model c-12D10 I'm thinking of using this but only utilising 2 contactors but what amp transformer would this work with?
Being AC 50-60hz I'm hoping it wouldn't need 1amp or over but I don't know I can't use existing transformer from the old setup as it rated input is 415v.
If you had any idea that would be greatly appreciated.
Cheers Dave
If the contactor was made by Allen Bradley the C-12D10 info appears to say it's a 120v coil !Model c-12D10 I'm thinking of using this but only utilising 2 contactors but what amp transformer would this work with?
The contactors can be ordered with 24V AC coil but the code might have a K J?If the contactor was made by Allen Bradley the C-12D10 info appears to say it's a 120v coil !
Its rated correctly for the 3-phase motor, but not for your single phase replacement.100-C12*10
Allen-Bradley MSC-C - contactors. The Allen-Bradley 100-C12*10 is a 3-phase IEC rated contactor used for the control of electric motors. It is rated 2 HP at 230V and 7.5 HP at 460V. Conforms to IEC/EN 60947-4-1 / 5-1 AB C12 10 AC Operating Coil Voltage: Options listed belowother 100-c contactors...controlparts.com
I think the coil current will be well under 1A, but I haven't seen its current consumption mentioned in the data sheets.
Does the existing low voltage transformer not have a primary tap for 220/240V as well as the 415V connection?