Afternoon, here's the proposed setup I am planning to supply 9 off 600w IR heating panels from a ring final circuit

the installation is commercial and the panels will be fitted to a suspended ceiling

a contractor and thermostat will control the heaters

the circuit is fed from a 32a rcbo

in the ceiling from the ring there is a fused connection unit 13a feeding and a 4 way hager click ceiling junction this then connects via the click system to 3 heaters (separate click connections) via 1.5 heat resisting flex

as there are 9 heaters 3 in each row this is repeated 3 times so from the ring there is a fused connection unit feeding each click box the ring legs will be equal due to the positioning of each click unit in relation to the consumer unit

the cables are clipped direct standard 2.5 twin and earth

anyone see any issues as it's slightly off a standard arrangement ?

thanks
 
The hager klik system is designed to control lighting,I would suggest you contact the manufacturer for approval to use the system for heating or use something else. As they are luminaire supporting couplers 559.6.1.4 prohibits their use for any other purpose.
 
The hager klik system is designed to control lighting,I would suggest you contact the manufacturer for approval to use the system for heating or use something else. As they are luminaire supporting couplers 559.6.1.4 prohibits their use for any other purpose.

Just read it thanks for that obvious now incase someone clicks a luminaire to it I suppose, I'll do it using standard plug and socket arrangement I'm looking and modifying a redundant circuit that's the reason I'm contemplating it

thanks
 
Why use an rcbo when the cable is running above a cieling , ,do the ceiling heater not have high and low setting . Just check the reg on ring final circuits at the back of the byb i sure that it says that ring final circuit should not run for long periods of time on a high load or somthing along those lines but with your set up of about 25amp you may be ok
 
Last edited:
cables are clipped direct standard 2.5 twin and earth

Looking at the regs, the green book, not the yellow - means I have to walk out to the van to get it, the current carrying capacity is 27A, your rcbo is 32A.

this means your exceeding the rating of the cable before the rcbo trips. follow 'flanders' advice you need to rate this circuit around 25Amps.
 
What i'd be inclined to do would be to mod the rfc into 2 radials, each @ 20A, feeding 3 heaters each. Then bung in a 3rd radial for the last 3. that would break it down better. ( That's if you can't split the existing into 3 ).
 
Last edited:
cables are clipped direct standard 2.5 twin and earth

Looking at the regs, the green book, not the yellow - means I have to walk out to the van to get it, the current carrying capacity is 27A, your rcbo is 32A.

this means your exceeding the rating of the cable before the rcbo trips. follow 'flanders' advice you need to rate this circuit around 25Amps.

Wtf? Ring finals have been fused at 32A for many many years without an issue, what new change in the rules do you think has de-rated the arrangement to 27A?
 

Reply to Dedicated ring final used to serve heating panels ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
998
Hi, I know it's best practice to run an immersion on a dedicated circuit but am I OK with the following A new heat pump is being fitted and it...
Replies
7
Views
2K
HI All, I am building a new house (self build) and have my part P so am running the cabling. My reading of the regs says that any appliance of...
Replies
18
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock