Hi All,

I'm installing a building management system in a domesticproperty with UFH and sorting out the temporary lashed-in control system. Somewiring centres (like the Emmetti) have a manifold pump delay, and some like theheatmiser don’t.


Is it essential to have, or can a Grundfos UPS2 pump copehappily when running in a closed environment while the electrothermic heads areslowly opening?

I’ve seen both used, but was just wondering whether itcan do pump damage….
 
Hi fella,there are a few situations, where non-positive displacement circulators can run with no flow. It is not efficient,desirable,and is an indication of a poorly designed system.

Why is this pump,in your system,not returning?
 
Hi fella,there are a few situations, where non-positive displacement circulators can run with no flow. It is not efficient,desirable,and is an indication of a poorly designed system.

Why is this pump,in your system,not returning?

I think you've expressed what I thought. I'm going to put a delay-on timer on the pump then so that the zone valves are open before the pump runs.

Cheers.
 
I think you've expressed what I thought. I'm going to put a delay-on timer on the pump then so that the zone valves are open before the pump runs.

Cheers.



Cant the plumber just pipe in a bypass? I prefer to keep/build as simple as possible.
e0045f3fcdfdff729a742b316472a6a4.jpg
 
Last edited:
Cant the plumber just pipe in a bypass? I prefer to keep/build as simple as possible.

Agreed simple is good!
This is the pump mounted on the UFH manifold, which makes a noise when it runs before the electrothermic heads open. There's nowhere for the water to go until they open and they take a few mins. The boiler bypass can't assist with that can it?
 
I've wired a couple of danfoss systems recently and they both switched the pump when any of the room stats closed.

As you've said, a delay-on timer on the pump would save it pumping against a closed valve.

Out of interest, those ufh actuators don't need the pump pressure to open do they?
 
..........

Out of interest, those ufh actuators don't need the pump pressure to open do they?

That's a good point I'd better check that.... I'll have a play on Monday and see. The trouble is there are 4 manifolds/pumps in this room and the noise is noticeable when it starts up. Then I'll rip all the crap out. There's 21 controlled zones and the plumber 'wired' it all using 8 of those crap Honeywell chocblock boxes in a seemingly random way.
 
I don't see the need for the pump delay? At the most it'll be a minute before the valves open and if there is 21 controlled zones is more than likely that one will be open when others are shut.
 
Agreed simple is good!
This is the pump mounted on the UFH manifold, which makes a noise when it runs before the electrothermic heads open. There's nowhere for the water to go until they open and they take a few mins. The boiler bypass can't assist with that can it?


Ahh got you. Is there no way of slightly altering it so the bypass could sit after the pump but before the manifold cut in between the Flow and return?
 
I don't see the need for the pump delay? At the most it'll be a minute before the valves open and if there is 21 controlled zones is more than likely that one will be open when others are shut.

Sometimes yes, sometimes no and when its no its noisy especially when more than one is doing it.
 
Would be interesting to see what manifold you have,i have had "built-up" systems,which have a by-pass included. There are ,supplied multi-zone manifolds,with in-built by-passes fitted.

I have seen countless set-ups,where circulators (pumps in pub-speak),spend hours stop-ended,when valving,either thermostatic or solenoid operated,closes off flow to satisfied zones. Some protest,whilst others merely struggle on,saved only by their membership of the non-positive displacement club :shocked3:
 
I have seen countless set-ups,where circulators (pumps in pub-speak),spend hours stop-ended,when valving,either thermostatic or solenoid operated,closes off flow to satisfied zones. Some protest,whilst others merely struggle on,saved only by their membership of the non-positive displacement club :shocked3:

Well the pump manufacturers say "its not that good but would be OK". How about that for a scientific answer! However as it makes a noise I've had to build a panel anyway I decided to use some delay-on relays. Although as mentioned previously on the thread, simple is good, the place is so complex anyway that it needs someone intelligent to maintain everything. 32 centrally mounted dimmers, DALI, KNX, Cat6, iPad control, HDMI matrix etc etc. Not bad for a house......

Thanks all for the input.
 

Reply to Delay on UFH Pump in the Central Heating Systems area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
951
I have a customer with a problem of RCD tripping caused by the wet UFH systems. There are 5 UFH areas each with a Wilo Para pump attached. Along...
Replies
29
Views
6K
Thought this might be of interest and use to anyone looking to undertake the various short training courses. So here is my recent experience -...
Replies
11
Views
4K
S
Esteemed forum Members, I had a 4kW Solar PV system installed in Dec ‘13 and since Feb and on an increasing basis with improving sunshine, I’ve...
Replies
14
Views
8K
S
J
View From The Site - The Old Breed I received an email this week asking if I can post this article up on here. A view from the site. Written by...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock