A circuit for a mig, at the point of use there is an fused isolator a 30A cartridge Bs88, at the DB is a 32A C RCBO the cables are in trunking and conduit will this meet the requirement for discrimination or am I misinterpreting 536.1 & 536.3
Pict
 
Will it discriminate? No I don't think it will, the question is does it matter if it doesn't? I don't think it does matter ( I take it this is a dedicated circuit).
 
I can't see the point in taking it away mate as long as its rated ok for the load. Additional point of isolation it will serve as.
 
Why does the owner want to remove the switch fuse> you will need local isolation surely
 
I want to bin it, (its an old ottermill about the size of a phone box) and replace it with a non fused iso , I think the old boy has some sort of sentimenal attachment to it, but as woz says its doing no harm as it is
Pict
 

Reply to Design question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock