A circuit for a mig, at the point of use there is an fused isolator a 30A cartridge Bs88, at the DB is a 32A C RCBO the cables are in trunking and conduit will this meet the requirement for discrimination or am I misinterpreting 536.1 & 536.3
Pict
Will it discriminate? No I don't think it will, the question is does it matter if it doesn't? I don't think it does matter ( I take it this is a dedicated circuit).
I want to bin it, (its an old ottermill about the size of a phone box) and replace it with a non fused iso , I think the old boy has some sort of sentimenal attachment to it, but as woz says its doing no harm as it is