Hi, first question on here in a very long time, I am hoping for some nice replies ?.
It's been playing on my mind all week and can't seem to find the answer anywhere I'm hoping this is the right place.
I want to run an armoured cable from a TNS supply to a consumer unit, the consumer unit is over 3metres so would be installed with an 60A switched fuse, the main cutout is 100A. (tails from DP isolator, from isolator into switched fuse unit, then swa from switch fuse to consumer unit)
It is a TNS supply and unluckily the Ze reading is 0.8ohms. This reading already exceeds the allowed for the 1361-2 fuse of 0.54 for 5 second disconnection. (80% OSG values).
Where do I stand here? Would I have to provide fault protection with an RCD? for example a 100ma stype and note it on the test sheet? So, swap the 100amp main switch in the switch fuse with a 100ma 100amp rcd?
Going forward, when designing should I always design with the higher 0.8 ze figure for all my tns work, as in theory although extremely unlikely it could rise to that and be OK. Which would have adverse affects on the installation? And likewise 0.35 for a TNCS?
I've always took a Ze measurement at the origin before designing and used that but I've been probably over thinking and can't figure out what to do.
Be nice please haha.
Cheers
It's been playing on my mind all week and can't seem to find the answer anywhere I'm hoping this is the right place.
I want to run an armoured cable from a TNS supply to a consumer unit, the consumer unit is over 3metres so would be installed with an 60A switched fuse, the main cutout is 100A. (tails from DP isolator, from isolator into switched fuse unit, then swa from switch fuse to consumer unit)
It is a TNS supply and unluckily the Ze reading is 0.8ohms. This reading already exceeds the allowed for the 1361-2 fuse of 0.54 for 5 second disconnection. (80% OSG values).
Where do I stand here? Would I have to provide fault protection with an RCD? for example a 100ma stype and note it on the test sheet? So, swap the 100amp main switch in the switch fuse with a 100ma 100amp rcd?
Going forward, when designing should I always design with the higher 0.8 ze figure for all my tns work, as in theory although extremely unlikely it could rise to that and be OK. Which would have adverse affects on the installation? And likewise 0.35 for a TNCS?
I've always took a Ze measurement at the origin before designing and used that but I've been probably over thinking and can't figure out what to do.
Be nice please haha.