Discuss Designing with diversity on sockets in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
31
Could somebody put into lamens terms for me what the diversity is on final circuits (sockets) as per table A2 in the OSG.

It reads:
"100% of current demand of largest circuit +40% of current demand of every other circuit".

Does "largest circuit" mean longest length, most sockets, or biggest demand?

Would you then work out what load would be on the largest circuit and add that to 40% of the total load on the other circuits?

Finally would that effectively mean you would apply the same load when calculating cable size to each final circuit?

I think i've i've over read this and confused myself DOH!

In simple terms i'm working through the design process for a simple 2 bedroom house, a ring final upstairs, a radial downstairs and a ring final for the kitchen + radials for oven/hob etc it's just the sockets i'm getting confused with what diversity to apply.

Many thanks in advance
 
say you have multiple rings on a 32A mcb type b


Then 100% (32A) for that ring
Other ring would be at 40% (32 × 0.4 = 12.8A)

32 +12.8 + 12.8 ect
 
That OSG max demand/diversity calculator is a little out of date, all well and good when granny had a couple of three bar heaters chugging away and a few 60 watt incandescent lamps heating the planet up.

Think about what actually runs domestically from a socket circuit.

In bedrooms there's the odd alarm clock, bedside lamp, TV, phone charger, toothbrush charger, shaver socket, occasionally the odd hair dryer and curling tongs etc. So realistically no more than say five amps.

In living areas you have the usual TV, DVD player, possibly computer, internet router, standard lamps, phone chargers etc. Again not a massive amount say around another five amps.

The odd time you may get the vacuum cleaner running around.

Kitchen is where you have your bigger appliances with larger current draw. So kettle, washing machine, dishwasher and tumble dryer. I've left an oven and cooker out of this for now as they would normally be on their own circuits. The appliances rarely run at the same time so potentially your could base your calculation on your highest rated device and add 50% for good measure. Say around 15 amps.

So there you have a basic domestic property drawing around 25 amps at a guess, TBH they're normally a lot lower than that.

This doesn't take into account electric showers, heating, instantaneous water heaters etc.

Maximum demand is really a 30 minute snap shot at one moment in time. You will get the odd spike when the tumble dryer and kettle are running at the same time then Doris decides to do the ironing whilst Desmond is hoovering upstairs, but how often does that happen?

By looking at maximum demand you can then start to work out your diversity and how to balance your circuits for maximum effect.

And then use a bit of SWAG, scientific wild arsed guess...

TBH general use sockets in a two bed domestic property you could get away with a couple of 20 amp radials with a 32 amp RFC for the kitchen/utility room.
 
say you have multiple rings on a 32A mcb type b


Then 100% (32A) for that ring
Other ring would be at 40% (32 × 0.4 = 12.8A)

32 +12.8 + 12.8 ect
I don't think that is how to apply diversity. As far as I know you should assess the expected loading of the circuits and then apply diversity . I know it's a misunderstood process but you definitely don't just subtract 60% of the mcb rating.
 
It seems to be a little confusing as you can apply diversity when it comes to individual circuits i.e a cooker circuit but then there is also the diversity you would apply to work out the Maximum demand of the whole installation (what you enter on the installation certificate).

Most the circuits are easy to calculate and you can either use actual loads if you know them or can use the book methods but its the socket circuits because if I calculated it the way the book states my socket circuits have the potential demand of 64amps which bumps up my maximum demand to 100amps when my fuse is rated at 80.... thats just not realistic or close to being realistic unless a heater was plugged into every socket.
 
It seems to be a little confusing as you can apply diversity when it comes to individual circuits i.e a cooker circuit but then there is also the diversity you would apply to work out the Maximum demand of the whole installation (what you enter on the installation certificate).

Most the circuits are easy to calculate and you can either use actual loads if you know them or can use the book methods but its the socket circuits because if I calculated it the way the book states my socket circuits have the potential demand of 64amps which bumps up my maximum demand to 100amps when my fuse is rated at 80.... thats just not realistic or close to being realistic unless a heater was plugged into every socket.
I use the rule of thumb, just bang it in .;)
 
It seems to be a little confusing as you can apply diversity when it comes to individual circuits i.e a cooker circuit but then there is also the diversity you would apply to work out the Maximum demand of the whole installation (what you enter on the installation certificate).

Most the circuits are easy to calculate and you can either use actual loads if you know them or can use the book methods but its the socket circuits because if I calculated it the way the book states my socket circuits have the potential demand of 64amps which bumps up my maximum demand to 100amps when my fuse is rated at 80.... thats just not realistic or close to being realistic unless a heater was plugged into every socket.
That is why you don't try to calculate it that way,If you calculate it that way then you will find many consumer unit's that are protected by a 100 amp main switch but the demand after the incorrect diversity calculation is still more than 100 amps
 
That is why you don't try to calculate it that way,If you calculate it that way then you will find many consumer unit's that are protected by a 100 amp main switch but the demand after the incorrect diversity calculation is still more than 100 amps

Yes this is what I am finding, how do you calculate the maximum demand for the socket circuits?
 
Yes this is what I am finding, how do you calculate the maximum demand for the socket circuits?
You assess the expected load and apply diversity to that figure,for example if you have 2 socket circuits then 100% of the first circuit is 32 amps and you then assess the second circuit and what is the expected loading if the second circuit?
There is a good video by John ward on YouTube that may help you because he does the sums and explains it very straight forward and simple.
Search diversity John ward on YouTube
 
You assess the expected load and apply diversity to that figure,for example if you have 2 socket circuits then 100% of the first circuit is 32 amps and you then assess the second circuit and what is the expected loading if the second circuit?
There is a good video by John ward on YouTube that may help you because he does the sums and explains it very straight forward and simple.
Search diversity John ward on YouTube
post 6#done keep up at the back .:D
 
Could somebody put into lamens terms for me what the diversity is on final circuits (sockets) as per table A2 in the OSG.

It reads:
"100% of current demand of largest circuit +40% of current demand of every other circuit".

Does "largest circuit" mean longest length, most sockets, or biggest demand?

Would you then work out what load would be on the largest circuit and add that to 40% of the total load on the other circuits?

Finally would that effectively mean you would apply the same load when calculating cable size to each final circuit?

I think i've i've over read this and confused myself DOH!

In simple terms i'm working through the design process for a simple 2 bedroom house, a ring final upstairs, a radial downstairs and a ring final for the kitchen + radials for oven/hob etc it's just the sockets i'm getting confused with what diversity to apply.

Many thanks in advance
Ashley Banjo will know all about "Diversity"
 
I don't think that is how to apply diversity. As far as I know you should assess the expected loading of the circuits and then apply diversity . I know it's a misunderstood process but you definitely don't just subtract 60% of the mcb rating.

I never said to just subtract 60% the figures are in the onsite guide, i just used what the OP had posted ie 40%.

Ive recently passed the design section on my apprenticeship & we we're tought that unless you can guarantee ie know for certain what is going to be plugged into the ring or radial then you go by the protective device rating & then apply diversity
 
I don't think that is how to apply diversity. As far as I know you should assess the expected loading of the circuits and then apply diversity . I know it's a misunderstood process but you definitely don't just subtract 60% of the mcb rating.

I never said to just subtract 60% the figures are in the onsite guide, i just used what the OP had posted ie 40%.

Ive recently passed the design section on my apprenticeship & we we're tought that unless you can guarantee ie know for certain what is going to be plugged into the ring or radial then you go by the protective device rating & then apply diversity
 
I never said to just subtract 60% the figures are in the onsite guide, i just used what the OP had posted ie 40%.

Ive recently passed the design section on my apprenticeship & we we're tought that unless you can guarantee ie know for certain what is going to be plugged into the ring or radial then you go by the protective device rating & then apply diversity

I applied the OSG method to the 2 ring finals and 1 radial (32 + 40% of 32+16) and then applied 100w per light fitting to the lights and did the loads for the actual boiler and oven (plus 5a for socket) and it all comes in at 77a so just less than the 80a fuse so i will put that on the certificate even though 51 amps for the socket circuits is crazy haha.

Thanks for the help people not been on the forum for long but its proving really useful :):):)
 

Reply to Designing with diversity on sockets in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
1K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
719
Hi. I'm in the process of getting my qualifications and am taking on some small jobs for family to try and get some experience in. Today I was...
Replies
17
Views
834
I'm looking at a vending hot drinks machine 2.9kW that has a thermostatically controlled hot water tank permanently attached to a water supply...
Replies
2
Views
232
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock