Darkwood

Staff member
Mod
Esteemed
Arms
Supporter
Reaction score
10,209
Just been handed a PIR done on a local factory for pricing of remedials, Remedial item no'9 - DB2 prospective fault current too high.
Now having 160amp BS88(2) and a ELI of 0.14 which is well within acceptable levels - im totally scratching my head. To further this hes put for above item in his pricing that to improve external loop impedance an additional 16mm earth will need to be run with the 70mm-4core armoured. So as i clock this guys attempt to understand ELI -He thinks PSCC is too high so to rectify it hes adding additional earthing to lower impedance values which eeeerrrrmmm! will make it HIGHER!
The front end 160amp fuses are 80Ka capacity so again well above the 2.8ka hes measured. Have i hit that age where ive gone stupid here or what?:90:

Lastly this is on official NICEIC cert so im assuming hes passed his exams on self test.... understanding the basics tends to be a good start when testing me thinks.
 
Maybe he just likes trying to get his ELI into single figures.
I don't suppose this is the only trade with more than it's fair share of muppets working.
 
Same guy condemned a dist' board for been disconnected not in use and requires removal, i checked it out to price and found 3phase supplies chopped off further back but neutral looped from previous board and acting as a borrowed neutral for 5 light fittings, plus a multigang light switch mounted underneath and into said board was still live and using board as a kinda of ducting to get from A to B, isnt it dangerous set ups like this that a PIR should high-light.
Just opening the other dist board and seeing a neutral supply loop in and the out would start ringing bells.
 
QUOTE Just been handed a PIR done on a local factory for pricing of remedials, Remedial item no'9 - DB2 prospective fault current too high.
Now having 160amp BS88(2) and a ELI of 0.14 which is well within acceptable levels - im totally scratching my head. To further this hes put for above item in his pricing that to improve external loop impedance an additional 16mm earth will need to be run with the 70mm-4core armoured. So as i clock this guys attempt to understand ELI -He thinks PSCC is too high so to rectify it hes adding additional earthing to lower impedance values which eeeerrrrmmm! will make it HIGHER! QUOTE




Whats the ELI got to do with the PFC?....He's not stating the PEFC is too high but the PFC,what value has he given for that?
 
Last edited by a moderator:
In the report as stated above hes put in remedials no9' DB2 (busbar chamber) prospective fault current too high. Then on his quote for work to be done hes highlighted remedial no' 9 and said this can be rectified by running additional 16mm earth to DB2 to improve external earth loop.

Cert says 160amp bs88-2 fuses for which he says permitted 0.2ohms (i thought it was 0.27ohms)

His reading for he gets is 0.14 well within either permitted.

The point im making is hes getting confused about what is what , the external fault loop cant be too high as the higher the better but it can over-rate fault current capacity of some protective devices where in this case it has a bs88-2 with a 80ka capacity.
The system is a TNCS

But point taken about pfc, pefc and eli reread it and its come across wrong was trying to express his thinking on that part not mine.
 
Last edited:

Reply to Didnt think id see this in a report. in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi First time with this kind of a job for me. I have a scenario where i am planning to install about 50m 25mm TPN from a TNCS supply to supply a...
Replies
32
Views
6K
Is there a room in professional PAT testing for a business model other than 'per unit'? I ask because I've been giving this some thought. I've...
Replies
40
Views
9K
F
Due to work increasing substantially, we are looking into employing a couple of members of staff rather then just sub contracting (one of the...
Replies
13
Views
2K
Megavolt
M
J
Hi All Im looking for a little bit of general guidance with regards to prices i should be paying for works. Without giving to much detail, I run...
Replies
31
Views
4K
1shortcircuit
1
O
Hey guys......more help with pricing would be appreciated....the prices im comming up with seem low but then the jobs didnt exactly take long...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock