If you have a fault from line to earth then this will trip the RCD, it would not matter if the neutrals were in place or not.
You could also have a neutral to earth fault that is then tripping the RCD as the current through the load to the neutral to earth fault will still be enough to trip the RCD.
Since the RCD trips all the time then you need to eliminate anything plugged into the circuit and then test the circuit, there should be a clear and obvious low IR result somewhere.
You could also have a neutral to earth fault that is then tripping the RCD as the current through the load to the neutral to earth fault will still be enough to trip the RCD.
Since the RCD trips all the time then you need to eliminate anything plugged into the circuit and then test the circuit, there should be a clear and obvious low IR result somewhere.