If you have a fault from line to earth then this will trip the RCD, it would not matter if the neutrals were in place or not.
You could also have a neutral to earth fault that is then tripping the RCD as the current through the load to the neutral to earth fault will still be enough to trip the RCD.
Since the RCD trips all the time then you need to eliminate anything plugged into the circuit and then test the circuit, there should be a clear and obvious low IR result somewhere.
 
Ok, I swung by on way home and sure enough the ze at the origin is 3.5 ohms so all four flats are affected. Have emailed my office saying as a matter of urgency we need to contact the supplier.
I always thought that a rcd looked for an imbalance between neutral and earth,and a mcb took care of overcurrent and short circuit and earth fault, hence being stumped after removing all neutrals from the board and even removing the outgoing neutral from the rcd and the rcd still tripping
 
An RCD does not look for an imbalance between neutral and earth, it doesn't have an earth connection, and you'd have serious issues if there was a balanced current across neutral and earth!
 
Sorry, I wrote that very quickly and without reading before sending, I meant it measures the return via the neutral which should be equal to the line conductor, any leakage via the earth will trip the rcd.
 
You say you havent done the IR testing yet. Instead of clutching at straws, start at the beginning. Do your continuity tests, IR and see what these highlight, it may put you straight to the answer. Generally, if you do things in the correct sequence it may appear to a be bit time consuming, but overall it will generally be quicker than starting in the middle and best guessing, not to mention forgetting what you have already tested. You may find a high resistance that might only be a loose connection, but enough to upset the RCD and trip it out.

Cheers................Howard
 
Ok, I swung by on way home and sure enough the ze at the origin is 3.5 ohms so all four flats are affected. Have emailed my office saying as a matter of urgency we need to contact the supplier.
I always thought that a rcd looked for an imbalance between neutral and earth,and a mcb took care of overcurrent and short circuit and earth fault, hence being stumped after removing all neutrals from the board and even removing the outgoing neutral from the rcd and the rcd still tripping
Hi Pondy,an RCD does monitor and operate due to an imbalance,but between line and neutral,this may be shootin' up THE earth,or AN earth,but it determines "some",maybe 30 ma's worth is awol,and operates accordingly. The advice concerning the order of tests is sound,and although on occasion skipping some can still bring a quick result,in general it negates back-tracking. Happy hunting.
 

Reply to Didn't think was possible in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
906
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
848
Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
1K
OLDBOY
O

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock