Hi every one, I had a bedroom light switch replaced with a dimmer by a qualified electrician some months ago and want to get another in another room. Before tackling this myself I thought I’d look at the bedroom dimmer as a guide after reading up about dimmers online. Just two wires so looks simple. The one I have has been fitted into a 16mm backbox though manufacturers say min box is 25mm, should I add a 10mm spacer? What, if any difference will this make. When I use a voltage detector on the switch it detects voltage when switch is on, and off. Is this correct, it’s a push on/off dimmer. Any help appreciated by one confused amateur.
 
you have a permanent live in C and switched live in L1. fit a spacer as this will help prevent the dimmer from overheating, apart from the fact that some dimmers will not physically fit in a 16mm box. wire up same as the existing switch. if the dimmer is metal faced, then you need to connect the cpc (earth) to the terminal on the faceplate instead of (or as well as) the back box. isolate the whole installation (main switch) before starting.
 
Thanks telectrix, not using metal faced dimmer and am ok about isolating. Do the permanent and switched lives mean the voltage detector always find voltage even when switch is off? Thanks again. Also thinking of using 25mm backbox when redecorating but spacer will be ok for now.
 
I would use a 35mm box for any dimmer. Gives enough room for the dimmer module and ensures the wires are not crushed behind the module when the plate is fixed back.
Your use of a voltage detector (of unknown type) sounds a bit haphazard and worrying. If you don't know why it would be live with the switch off you would be better not taking risks and calling someone in to fit it for you.
 
Hi Andy78. I appreciate your concern but am quite happy to fit myself as I’ve fitted rocker switches quite safely before. A 35mm box would be ideal but I think a spacer will do as it meets manufacturers specs re space. Thanks for your help.
 

Reply to Dimmer switch installation questions in the Lighting Forum area at ElectriciansForums.net

Similar Threads

our dimmer switch stopped working after 7 years so went to replace it at the weekend. When I opened it up, the black wire was in the common slot...
Replies
0
Views
230
I have carried out home wiring for 60 years as a competent person, for the last 20 years, I employ a local electrician to check my work and sign...
Replies
10
Views
1K
DIY query Have narrowed down the source of an occasional trip to one light circuit which is a varilight v-pro master dimmer slave set up. This...
Replies
0
Views
429
I really need help with this puzzler. First - I am moderately 'skilled' in day-to-day basic wiring. My puzzle: I am trying to replace a...
Replies
10
Views
1K
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
692

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock