Appletree - did the electrician actually use his eyes to study the wiring in the image? I suspect not. If one looks carefully at the two brown wires which are middle top and pass downwards once can see that the insulation on the left of the two has been scraped away revealing a small area of the copper conductor. I think there is similar damage to the right hand brown conductor - and I looks to me as if they may have been touching at these points before the switch plate was moved forward. Both these brown conductors are switched lives. The right hand one goes to L2 and almost certainly the left hand one goes to L2 on the other dimmer.

So, please take another look and take some photos from a different angle to confirm my observations. You will need some brown sleeving to cover the damaged areas. DON'T GO STICKING YOUR FINGERS IN WITHOUT TURNING OFF THE ELECTRICITY FIRST
 
Last edited:
changing to a normal on,off wont work. We have the same issue where switching off and on a toggle in one room causes a flicker to present itself as you toggle on. random LED's in the adjacent room flicker. this problem wasnt there when the lights were plain ballast 4 bulb lay in fixtures.

they are direct wire, no ballast, led lights. No dimmers ever involved in this.
 
That's probably on a two way switched circuit?
no, there is only what I just told you. I am an electrician. So I didnt leave out anything obvious.

I have read online some people saying that you cant have two low voltage control units connected within the same junction box, because of induction.

I believe that switches are truthfully still allowing voltage to seep, and while old lights dont see it, an LED can, and this has cause havoc in commercial settings.

one guy said to put a resister wired inline with the switchleg and it will bleed away (peel off, thwart, whatever word you want to use) errand voltage that makes it past the switch.

But thats doing too much as far as I'm concerned, I'd just as soon do away with the stupid controllers all together. They cost too much anyhow.
 
I'm sure it worked.
But its like, when installing them, if people in the field, have to add things onto the product to assure there is no potential for customer call back, then that product needs to be doing that addition from the factory.
Because knowing that the potential for flickering lights exist, and a customer would see that as "the electrician wired up something crazy"
then one has to explain that its the device, thats just doing too much.
 
For those that are interested, I should have said Capacitors not Resistors, can't seem to find them on the RS web site at the moment, but "RIFA PMR209" was their reference and are the same width as the inside of a Wago lighting box makes for a very neat installation.
 

Reply to Dimming lights in one room makes lights in another room flicker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am not an electrician but am looking for some advice as to how to fix my sporadic light flickering problem that has come and gone for the year...
Replies
24
Views
2K
Hello, I added a 240v insta hot water heater at the kitchen sink. When the water heater is in use the lights in the adjacent dining room flicker...
Replies
1
Views
816
My son is having a new house built. The electrical wiring is almost complete but a problem has been detected. Some of the rooms LED lights...
Replies
3
Views
1K
Hi :) I'm currently renovating my outbuilding. My electrician has fitted 10 conduit LEDs (that support both leading and trailing edge) and x4...
Replies
0
Views
231
Sure this has been answered before, can’t find a specific answer though. My house was rewired in 2021 and as part of the rewire I had LED lights...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock