Discuss Dimplex Quantum storage heater 150 - keeps melting 20amp double pole switch in the DIY Electrical Advice area at ElectriciansForums.net

Reaction score
2
Had a quantum (qm150) installed for 8 years - no problem.
Couple of weeks ago the switch (usually always on except when on holiday) stuck and no power to heater.
Had a look at switch and saw it was melted where the N wire goes in.
Bought an exact replacement (B+Q) and replaced myself with the same wires (one from E7 and one set from normal switches in house)- worked fine for about 10 days and then suddenly has stuck again with same N wire melted.

When researching on here for the problem, it was suggested that the switch may be at fault and to replace, which I did.

My question is now- should I replace with another 20amp double pole switch (maybe a better brand?) or should I use something else (Im not skilled at electrics beyond wiring plugs/replacing sockets etc) instead ?
Or is it a bigger job that need an a qualified electrician to look at ?
Like I said, it has been fine with no problems for 8 years, till now.
 
For the size of heater, any 20A double pole switch should be ok.

Heating up at the terminal usually points to a loose connection.

If the cable has burned before… it’s better to cut off the burned end off and restrip the end to clean copper.
 
For the size of heater, any 20A double pole switch should be ok.

Heating up at the terminal usually points to a loose connection.

If the cable has burned before… it’s better to cut off the burned end off and restrip the end to clean copper.
Cheers.
It was exact same one I replaced- will try stripping the end like you suggest and putting in a new one and get back.
 
Just another note.

If it’s a single core of cable, strip about an inch off, and fold it over. Fills the terminal hole better, and gives the screw two surfaces to hold onto.

Too much stripped off, or not inserted fully will show bare copper, which we try to avoid.

Heating up can also occur where a live terminal is too close to an earthed metal back box.
Take care if the box has unused screw lugs top and bottom as well as on the sides. They can end up really close when the switch is screwed back, and are best bent flat.
 
Just another note.

If it’s a single core of cable, strip about an inch off, and fold it over. Fills the terminal hole better, and gives the screw two surfaces to hold onto.

Too much stripped off, or not inserted fully will show bare copper, which we try to avoid.

Heating up can also occur where a live terminal is too close to an earthed metal back box.
Take care if the box has unused screw lugs top and bottom as well as on the sides. They can end up really close when the switch is screwed back, and are best bent flat.
Good tip- bought some wire strippers for this purpose.
Cheers
 
Follow up- Replaced the melted switch and so far so good.
I only have the storage heater and the hot water tank on E7,
looks like it goes from the water tank to switch and then on to heater.
The hot water switch gets hot (but doesnt melt) and I have tightened up connections there also,
but still gets warm.
Could this be a problem?
 

Reply to Dimplex Quantum storage heater 150 - keeps melting 20amp double pole switch in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
205
Hi all. I have a customer, manager of a retirement home and he's having problems with the original heaters. The existing heating in the multi...
Replies
1
Views
1K
Replacing an old storage heater with a Dimplex Quantum Storage Heater, but the Dimplex is physically larger, placing it directly beside the power...
Replies
2
Views
1K
  • Sticky
Ferrets are known for being small, resourceful, and incredibly clever. They can solve many problems by fitting into tight spaces and doing jobs us...
Replies
4
Views
2K
Hello, I’m not an electrician and I have a question in relation to Dimplex Duo300n. Some background information: a couple of months ago I have...
Replies
34
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock