Discuss Disconnection times with off grid application. in the UK Electrical Forum area at ElectriciansForums.net

M

MRL

Hi All
New to this forum and fairly new to the business too.

I have a project I'm putting together which is an off grid house. There are two 5000VA inverters with sufficient battery size and a sizeable generator to switch in once loads exceed about 7kW, which will ADD a further 100A.

Here's my conundrum, but could be just numb brain. If the system is running on inverters only it can deliver a maximum of 10kVA/230V = 43A. The inverters will operate at 100% overload for 30 mins before shutting down, so the maximum fault current that can be delivered would be 2 x 43A = 86A. Every final circuit and the distribution is RCD protected but for overcurrent protection does such a low Ipf mean that MCBs above 16A will not achieve disconnection within the required time? Obviously such a demand would cause the genny to start and add current but the time this would take would be indeterminate.

Is setting all of the MCBs to 16A the answer, although it contravenes 433.1.1 (i) for some loads such as cooker and water heater.

Thanks
 
I'm thinking aloud here and may also just have a numb brain, but since nobody else has replied here goes: is 86A definitely the Ipf, or is that just the maximum current the inverter can handle safely, with the Ipf being much higher? Maybe something to think/read about, but don't just assume I'm right - I may be very wrong!
 

Reply to Disconnection times with off grid application. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All, Main issue is as per title: inverter is stuck in Off-Grid mode. I used Self Use over the summer, which worked well, priority PV order...
Replies
8
Views
5K
mididoctors
M
S
First off, I'm not a sparky, but I have done household rewiring, and I'm an electronics engineer, so I'm also used to dealing with AC / DC high...
Replies
10
Views
10K
siliconskum
S

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock