Piratepete

Morning Guys

I know that if a 100mA RCD is followed by a 30mA RCD, the 100mA needs to be S type.

If a 300mA RCD is followed by a 30mA RCD (Farm installation) does the 300mA need to be S Type?

Cheers

Pete
 
Yes. The mA value is irrelevant for discrimination. Think about what happens when there is a fault, follow its path, think about the speed of operation of devices, and the penny will drop
 
Yes. The mA value is irrelevant for discrimination. Think about what happens when there is a fault, follow its path, think about the speed of operation of devices, and the penny will drop

Cheers
Just looking for confirmation because of the extortionate price difference between standard and S type.
Pete
 
Yes they can be pricey!
But think, if you fitted a 300mA then a 30mA 100 metres away further along, and a fault occurs, which one will trip?

(Trick question)
 
Well, If we Have a leakage current of 300 mA, downstream of the 30 mA RCD, so we have the 300 mA TD first, then the 100 mA TD and finally the 30 mA.

1, 300 mA TD rcd
2, 100 mA TD rcd
3, 30 mA rcd

Which Rcd will trip?

Regards Chris
 
Last edited:
Morning Guys

I know that if a 100mA RCD is followed by a 30mA RCD, the 100mA needs to be S type.

If a 300mA RCD is followed by a 30mA RCD (Farm installation) does the 300mA need to be S Type?

Cheers

Pete

You often see statements like, ''The upstream RCD device needs to be a minimum of 3X the mA rating, that of the downstream RCD device to assure discrimination''!! If you follow this rule, your going to be sorely disappointed, because that statement is just pure folly and doesn't work in the real world!! It won't work with 10X the downstream mA rating either, and have personally known 30mA and 500mA devices tripping out together. The ONLY way to ''ENSURE'' discrimination between upstream and downstream RCD devices during a fault situation is by Time Delay on the upstream device...

In industrial and larger commercial installations, the use of adjustable RCD modules to give even greater control /closer protection on intensive RCD protected installation areas.... If you think S type RCD's are expensive check those babies out...lol!!! Both mA and time delay ....10mA to 1A rating settings and time delay 0 to 60 sec
 

Reply to DISCRIMINATION BETWEEN RCDs in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
664
Keeping this brief.....................New dwelling.....TT system with 100mA S type rcd protected supply to local board with 30mA RCD. Freelance...
Replies
21
Views
3K
Ok, most new Consumer unit seem to come with a 63A RCCB and two MCBs. Most house consumer units now will also have RCD of some type be it a dual...
Replies
24
Views
1K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
943

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock