Discuss DISTANCE from D/G socket to max reach of pull out kitchen tap ? in the UK Electrical Forum area at ElectriciansForums.net

LukeD

-
Esteemed
Arms
Reaction score
1,329
Distance from D/G socket to extended pull out kitchen tap ? Kitchen tap when pulled out is easily with 400 mm of a D/G socket . Not my job . Just asking for clarification etc
 
Don't think there is an actual stated distance in 7671. It would rely on the 'suitable for external influences' test. (Is it likely to be sprayed by the tap, etc).

Lots of bathroom zone pics online that show a zone around the tap but that's not actually based on anything in the Regs

There might be something in other guidance or building Regs...
 
Looks like Guidance Note 1 may say "It is preferable that accessories should not be installed within 300mm of a stainless steel sink unit top"

Though that's again not an absolute requirement...

According to this page, NICEIC guide and NHBC seems to state a minimum distance of 300mm....

Edit: Never seen this document before before, but the NICEIC guide to electrical work in the kitchen says

"Electrical sockets or switches should be fitted at a safe distance (it is recommended at least 30cm horizontally) from a sink to avoid the chance of water coming into contact with electricity."

Electrical Safety First also say:

"To avoid water coming into contact with electricity, make sure that your sockets or switches are fitted at a safe distance (at least 30cm horizontally) from the sink."

so looks like 300mm is guidance, but a good rule of thumb...
 
300mm is a recommendation not an absolute.
 
Seem to recall the guidance (which seems emanates from NHBC) has the 300mm figure from the bowl of the kitchen sink, and not including the draining board.
 
Its 450mm from the kitchen tap .But once that pull out spout section is extended . The spout can reach to 30mm from the socket .
 
Its 450mm from the kitchen tap .But once that pull out spout section is extended . The spout can reach to 30mm from the socket .
You can't design for what some idiot customer might do. If they're daft enough to spray water on a socket then they may be just as likely to pour a jug of water onto a socket. Or let the steam from a kettle spout be directed onto a socket.

The actual recommended distance of 300mm is horizontally from the edge of the sink/drainer.
 

Reply to DISTANCE from D/G socket to max reach of pull out kitchen tap ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
860
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
817
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Ok i may get slated for this one but here goes; A bit of background info first. Its been a while since ive looked at my iee regs, and ive not...
Replies
12
Views
2K
Hi Guys, I have the walls open (removing tiles from dot and dab walls fml...) Can i connect a single FCU 13a to both my integrated Fridge...
Replies
6
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock