Discuss Diversity factor and demand factor, confussion..... in the UK Electrical Forum area at ElectriciansForums.net

D

divobtech

Hi, could someone explain me the difference between sum of individual maximum demand and connected load.... do you think it is the same, ?

And the answer for this exercise is what exactly, ?I have some confussion in the calculation...

A power supply is having the following loads,

A domestic load with maximum demand of 1500kw, diversity of group is 1.2 and demand factor 0.8
What will be the connected load... ?

My answer is 2250 kw, could you confirmed this,

Thanks in advance.....
 
Thanks but not, it is impossible, the connected load must be always greater than that of the maximum demand.
The answer must be 1800kw or 2550kw ....
 

Reply to Diversity factor and demand factor, confussion..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
About 15 years ago, after having had a modern consumer unit fitted, and prompted by our electrician, I asked my then energy supplier (Tonik) if...
Replies
25
Views
5K
I recently had a discussion with another spark about induction hobs and diversity. He pointed out that an induction hob may have, for example, 4...
Replies
23
Views
10K
Could somebody put into lamens terms for me what the diversity is on final circuits (sockets) as per table A2 in the OSG. It reads: "100% of...
Replies
56
Views
21K
Hi all, I wonder if you might chuck in your 10 cents worth on this on? I have been asked to install electric heating in an office up on the 4th...
Replies
18
Views
3K
Toneyz
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top