- Reaction score
- 17,126
Evening, all.
I've got a kitchen coming up that might lead to more work with a local joiner... first job with him and I want to appear on the ball.
Current set up is 32A MCB on RCD side of a split board, 6.0mm serving a regular cooker switch with only an electric oven coming off it. Hob is presently gas.
The kitchen plan asks for a built in eye level oven and separate microwave combi at the current switch position and an electric hob further round the worktop, so the 32A supply would have to be extended.
The ratings are:
Microwave - 1600W for grill, 900W for microwave. Don't know if these fiunctions would operate simultaneously.
Regular oven - 3650W
Hob - 7200W
Both ovens run off a standard 13A plug, but to have these on the rfc along with kettle, toaster, washing machine and whatever else may be a push.
My plan was to have one of the ovens on the rfc, the other sharing the cooker circuit with the hob. Possible uprating of the mcb to 40A
I've got a kitchen coming up that might lead to more work with a local joiner... first job with him and I want to appear on the ball.
Current set up is 32A MCB on RCD side of a split board, 6.0mm serving a regular cooker switch with only an electric oven coming off it. Hob is presently gas.
The kitchen plan asks for a built in eye level oven and separate microwave combi at the current switch position and an electric hob further round the worktop, so the 32A supply would have to be extended.
The ratings are:
Microwave - 1600W for grill, 900W for microwave. Don't know if these fiunctions would operate simultaneously.
Regular oven - 3650W
Hob - 7200W
Both ovens run off a standard 13A plug, but to have these on the rfc along with kettle, toaster, washing machine and whatever else may be a push.
My plan was to have one of the ovens on the rfc, the other sharing the cooker circuit with the hob. Possible uprating of the mcb to 40A