Hi Guys,

I am just changing my plug top oven over & gas hob and noticed the following:

32AMP Breaker > 6MM Cable > Cooker Switch 45a > 4mm cable > Double Socket which powers both.

13a Plug Top Oven replacing the previous same plug top. Gas Hob and just powers the igniter.

Is this right or do i need a sparky in to replace this?

Thanks in advance!
 
The precise pernickety jobsworth answer is that whether the 4mm is ok between the isolator and the socket depends on the construction of the wall and how the cable is run. The rating for that cable varies between 17.5 and 37 amps depending on this!

BUT In reality you know exactly what the loads are, and they won't be changing once the new oven is installed, and the circuit is perfectly adequate for the loads even in the worst case scenario of the 4mm being surrounded by insulation in a stud wall.
I'm assuming the gas hob has a 3 or 5 amp fuse in the plug.

As far as you are concerned there is a double socket there that you have no reason to believe isn't to regs, so use it!
 
agree with above. plug and play. once you got the hang of it.let 'erindoors have a go. then you may need an electrician.🤣😘
 

Reply to Do I need an electrician in? 32amp to Cooker Switch to Double Socket. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I'm about to replace our kitchen and one of the upgrades is to install two full size ovens to replace the original twin over under...
Replies
7
Views
1K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
741
I have just had my kitchen redone and the kitchen rewired with a new 6mm cable installed for an electric cooker. However I have changed my mind...
Replies
10
Views
2K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
835
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
792

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock