Discuss Do I need to rewire? in the UK Electrical Forum area at ElectriciansForums.net

sydbardo

DIY
Reaction score
0
Hi
What would be your thoughts on this one?
I bought this property last year, it was rented since 2005.
EICR from 2016 states "wiring in fairly good condition".
EICR from 2021 states "wiring in average condition".
I am planning on full refurb of the property but won't be adding more electrical outlets to the existing ones. I will be removing power shower and getting thermostatic one and also getting rid of glasswasher. I will be adding spot lights only and non electric underfloor heating.
I don't get any of the aged electrics signs at all and would rather spend money elsewhere and yet want to have a safe property.
Is it necessary to fully rewire or would part rewire of the kitchen suffice?
Thank you very much for your time and opinion shared here.
 

Attachments

  • Screenshot_20230510_202225_com.xodo.pdf.reader.jpg
    211.7 KB · Views: 48
  • Screenshot_20230510_202237_com.xodo.pdf.reader.jpg
    121.9 KB · Views: 27
  • Screenshot_20230510_202240_com.xodo.pdf.reader.jpg
    251.3 KB · Views: 23
  • Screenshot_20230510_202242_com.xodo.pdf.reader.jpg
    66.3 KB · Views: 24
  • Screenshot_20230510_202254_com.xodo.pdf.reader.jpg
    243.6 KB · Views: 15
  • Screenshot_20230510_202257_com.xodo.pdf.reader.jpg
    270.4 KB · Views: 15
  • Screenshot_20230510_202308_com.xodo.pdf.reader.jpg
    208.9 KB · Views: 13
  • Screenshot_20230510_202311_com.xodo.pdf.reader.jpg
    110 KB · Views: 17
  • Screenshot_20230430_192911_com.xodo.pdf.reader_edit_18104083458695.jpg
    207.3 KB · Views: 15
  • Screenshot_20230430_192914_com.xodo.pdf.reader_edit_18134843135253.jpg
    253.5 KB · Views: 15
  • Screenshot_20230430_192933_com.xodo.pdf.reader_edit_18160819620666.jpg
    55 KB · Views: 15
  • Screenshot_20230430_192917_com.xodo.pdf.reader.jpg
    120.3 KB · Views: 14
  • Screenshot_20230430_192929_com.xodo.pdf.reader.jpg
    190.1 KB · Views: 12
  • Screenshot_20230430_192937_com.xodo.pdf.reader.jpg
    168.4 KB · Views: 13
  • Screenshot_20230510_214517_com.xodo.pdf.reader.jpg
    282.3 KB · Views: 46
Both reports say satisfactory though, that's good isn't it. I gather the consumer unit was upgraded since the 2016 EICR as that one stated 3871 breakers and the 21 reports says 60898's.
Saying that though, one socket circuit and one lighting circuit is a pretty basic spec and probably quite old, is it a small house. I will also bet that if you pull the floorboard up or in the loft there will be badly terminated junction boxes or even connectors everywhere.
 
Both reports say satisfactory though, that's good isn't it. I gather the consumer unit was upgraded since the 2016 EICR as that one stated 3871 breakers and the 21 reports says 60898's.
Saying that though, one socket circuit and one lighting circuit is a pretty basic spec and probably quite old, is it a small house. I will also bet that if you pull the floorboard up or in the loft there will be badly terminated junction boxes or even connectors everywhere.
Hi
2 bed 90m2
Floorboards will be refurbished too, so is it worth rewiring room by room and upgrading that single circuit when doing kitchen?
 
If you are redoing the kitchen then certainly put in a dedicated circuit for the kitchen sockets, maybe put a new lighting feed in for that as well. we always do this when we wire new kitchen/dining extensions, keeps it totally separate form the rest of the household electrics.
 
If you are gutting the house, taking up large portions of the floors then if it were my job I would take this opportunity to do a basic re-wire. get some mains smokes wired in and some nice modern lighting and USB sockets etc.
A small house won't cost the earth to Re-wire and it will future proof it for years to come
 
IR testing is highly likely to have been carried out correctly if at all as all results would not be expected to be that high if the cabling isn’t new or nearly new so it would be wise for I have a proper EICR carried out before proceeding.
 
IR testing is highly likely to have been carried out correctly if at all as all results would not be expected to be that high if the cabling isn’t new or nearly new so it would be wise for I have a proper EICR carried out before proceeding.
Dont you mean that
IR testing is highly unlikely to have been carried out correctly....
 
IR testing is highly likely to have been carried out correctly if at all as all results would not be expected to be that high if the cabling isn’t new or nearly new so it would be wise for I have a proper EICR carried out before proceeding.
Hi
It is good point however do you mean that both (2016 and 2021) EICRs look too good?
Please see this picture of exposed wires. How old do they look?
Thanks
 

Attachments

  • Screenshot_20230512_132132.jpg
    1.3 MB · Views: 35
Hi
It is good point however do you mean that both (2016 and 2021) EICRs look too good?
Please see this picture of exposed wires. How old do they look?
Thanks
The key indicator is the Insulation Resistance figure. The minimum allowed is 2Megohm. Older installations degrade over time from their initial installation results.
The report shows an IR figure of greater than 500Megohm on all circuits. That is a figure that is hard to get even on a newly installed installation. Therefore i wouldn't trust that any IR tests have actually been carried out and calls into question the validity of the report.

Re age of the wiring. The use of red/black as wiring colours ran until March 2006 when they changed to blue and brown.
Up until 1970ish the cables often had stranded conductors. If yours are solid conductors it in dicates the red&black wiring could be anything from 50 to 20 years old. the brown&blue flex is a later addition (I guess for a wall light?) .

So...do you need a rewire? If the cabling is in good condition and the IR tests are ok then the cabling is probably OK for a good time yet. But I dont believe the IR tests. So the answer is "maybe"
 
No where in BS7671 does it suggest a minimum value of insulation resistance for circuits when carrying out an EICR. The values given in Table 64 are for the purpose of initial verification.
 
No where in BS7671 does it suggest a minimum value of insulation resistance for circuits when carrying out an EICR. The values given in Table 64 are for the purpose of initial verification.
Well, yes. But I was trying to make a simple comparison for the OP to illustrate that the test results can’t be believed.
 
Hi
It is good point however do you mean that both (2016 and 2021) EICRs look too good?
Please see this picture of exposed wires. How old do they look?
Thanks
Yeah I would think so. Could be wrong but seems too good to be true in my experience. They look extremely rough and potentially have the cpc cut off. Definitely need a proper eicr done, wouldn’t rule out rewiring or not at this stage.
 
The key indicator is the Insulation Resistance figure. The minimum allowed is 2Megohm. Older installations degrade over time from their initial installation results.
The report shows an IR figure of greater than 500Megohm on all circuits. That is a figure that is hard to get even on a newly installed installation. Therefore i wouldn't trust that any IR tests have actually been carried out and calls into question the validity of the report.

Re age of the wiring. The use of red/black as wiring colours ran until March 2006 when they changed to blue and brown.
Up until 1970ish the cables often had stranded conductors. If yours are solid conductors it in dicates the red&black wiring could be anything from 50 to 20 years old. the brown&blue flex is a later addition (I guess for a wall light?) .

So...do you need a rewire? If the cabling is in good condition and the IR tests are ok then the cabling is probably OK for a good time yet. But I dont believe the IR tests. So the answer is "maybe"
Thank you
Yeah I would think so. Could be wrong but seems too good to be true in my experience. They look extremely rough and potentially have the cpc cut off. Definitely need a proper eicr done, wouldn’t rule out rewiring or not at this stage.
Thanks
I gather an E
Yeah I would think so. Could be wrong but seems too good to be true in my experience. They look extremely rough and potentially have the cpc cut off. Definitely need a proper eicr done, wouldn’t rule out rewiring or not at this stage.
Thanks
I gather a proper and full EICR test would be beneficial.
It feels though, that anybody who carries out these test, wants to have a further follow up works of rewiring, so their results would in most cases indicate that.
 
It feels though, that anybody who carries out these test, wants to have a further follow up works of rewiring, so their results would in most cases indicate that.
A way round that temptation to “create” work is to make it clear to the testing electrician that, he/she would not be doing any remedial works.
 

Reply to Do I need to rewire? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
890
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
709
HI , potential 2 bed 1970’s bungalow buyer here…. Our surveyor (RICS) has pointed out there is no circuit breaker to the electrics (fuse board...
Replies
16
Views
1K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock