This is how I was told to validate:

Let’s say my r1 is 0.20 rn is 0.20 r2 is 0.30

R1+Rn = r1+rn/4
R1+Rn = 0.20+0.20/4
= 0.40/4
= 0.10 ohms
So R1+Rn = 0.10 ohms

Then repeat for r1+r2 to validate the R1+R2 reading

I was not told to put anything in brackets

You've done the sum by doing the addition first. But in mathematical hierarchy (BODMAS) division is done before addition.

So thought you have done it in the correct order, it is actually written incorrectly.
 
You've done the sum by doing the addition first. But in mathematical hierarchy (BODMAS) division is done before addition.

So thought you have done it in the correct order, it is actually written incorrectly.
This is exactly how they told me to write it out on my revision day. Not sure what’s right/wrong now

GSH electrical have also done it the same as me and they’re college tutors
 

Attachments

  • 419FA466-5930-4EA4-A6EB-2D05DE5AB765.jpeg
    554.2 KB · Views: 10
GSH have written it as a fraction which is just another way. If you make sure you do the addition first, it will work or if your calculator lets you lay it out as GSH has. The equation is technically wrong without the brackets and all written on one line.

What you have written "R1+Rn = 0.20+0.20/4" = 0.25ohm
 
This is exactly how they told me to write it out on my revision day. Not sure what’s right/wrong now

GSH electrical have also done it the same as me and they’re college tutors

You don't need brackets when it is written with items above and below the line as they have done. But the way you wrote it is incorrect, ie. R1 + Rn / 4
 
This is exactly how they told me to write it out on my revision day. Not sure what’s right/wrong now

GSH electrical have also done it the same as me and they’re college tutors
That drawing is not the same as writing the equation in a straight line. In the drawing, the sum of r1+ rn is written above the divisor, which makes it obvious in which order to evaluate the equation.
When written in a straight line, we need to follow the rules of what order to do the evaluation, which is summarised using the acronym BODMAS, or BODMAS.
Just to back this up, page 66 of guidance note 3 shows the equation as (r1 + r2)/4, which clearly shows the use of brackets.
 

Reply to Do I use zdb or ze when calculating zs values on am2? in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

So I’m doing my level 3 design project at the moment, and I’m on the question where you do all the calculations on each circuit, I’ve taken the...
Replies
3
Views
2K
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock