you should be able to measure earth continuity from this point to the 13A plug, if no continuity then replace cable.
however I am surprised that you would plug it in after discovering a fault in the earth.
 
you should be able to measure earth continuity from this point to the 13A plug, if no continuity then replace cable.
however I am surprised that you would plug it in after discovering a fault in the earth.
I was unable to test the earth continuity...........my machine couldn't read it. Hence my query. I didn't plug it in, custmer insisted on doing so. And an electrician has apparently since been able to pass it. My query was why couldn't my UT528 test it? Was I doing something wrong, or was it outside my machine's capabilities?
 
You are misunderstanding, you should be able to measure the continuity of any piece of wire from one end to the other.
if you can’t read it on your tester, it is not there to read and is a fault either in your test method or the cable.
 
You are misunderstanding, you should be able to measure the continuity of any piece of wire from one end to the other.
if you can’t read it on your tester, it is not there to read and is a fault either in your test method or the cable.
Thanks for your patience James. I am new to this so maybe don't use the right words. I do of course understand that I should be able to measure the continuity of any piece of wire, and that is exactly what I was trying to do with my UT528 on this appliance. Usually when I test it gives me a reading, which I can then see is either a pass reading or a fail. However on this occasion the machine was just saying "fail", no reading in numbers at all, wherever I attached the probe on the casing, which was all metal. So I was unsure whether it was reading it at all! Or a genuine fault. As it was later passed by another technician I assume I was doing something wrong and was merely trying to find out from you guys what, if anything, I should have been doing. I tested the machine at home on our own fridge and it worked fine, so not the machine. I wonder if I was either not attaching the probe to the correct place, or whether I needed to reset the UT528 for a longer cable or different voltage?
Thanks again
 
I have seen issues before where people rely on the test instrument saying 'Pass' or 'Fail'. But a tester should know what results to expect, and what they may mean when they are outside limits. There may be a need to perform manual tests in some cases.
 
. As it was later passed by another technician I assume I was doing something wrong and was merely trying to find out from you guys what, if anything, I should have been doing.

It is at that point you just get your multimeter out and check for continuity between plug and the machines earth terminal and between the earth terminal and the suspect metalwork.
 

Reply to Does anyone use the UNI-T 528 test tool in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

I am trying to understand how a relay system works and have designed a circuit and a ladder diagram all as attached for an 8 PIN relay, a current...
Replies
14
Views
544
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
915
Hello all, First of all I apologise if this is in the wrong forum, I figured the general forum may be the best bet :) Thank you for taking...
Replies
3
Views
585
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
206
Getting desperate to clear my small garage, and I have a bit of old red/black T&E. I used a few bits to add a socket or two in my flat and a...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock