Search the forum,

Discuss Does freezing cold temps mean bad IR values ? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
0
i am testing 4 flats in the one close, high rise flats were being brought down next to them so tennants have been moved out for a few months, and its freezing cold in glasgow right now, when testing the house ring which is wired through conduit i am getting between 30 - 50 mega ohms going between each of the cables in each of the flats and they were rewired 2 years ago, would this effect the results ?
 
damp could be a factor, but with those readings, why worry?
 
Not sure what voltage your IR test was at but as Tel says 30-50 Megs is certainly not worth chasing especially if conditions are cold and damp.
 
It was done at 500V, i was just wondering because the flats have recently been rewired and the fact it is installed in conduit i would expect much better readings and because the flats were all giving roughly the same reading i was wondering if that would be the cause
 
Hi

Its quite common to find low readings in an unheated/damp enviroment. The readings are acceptable, if your worried advise to have a glbal IR test carried out when the flats are occupied.

Cheers
 
Lol, If you're really curious and have plenty of time on your hands you can go around one of the flats with a hair dryer and gently warm up the CU and accessories such as sockets, switches and light points and see if the global IR reading for that premises improves.
 
Lol, If you're really curious and have plenty of time on your hands you can go around one of the flats with a hair dryer and gently warm up the CU and accessories such as sockets, switches and light points and see if the global IR reading for that premises improves.
Can't. It was rewired 2 years ago meaning plastic cu's so that's a recipe for disaster. The 18th will have a new regulation 'only use a hair dryer to warm up cu's that are metal'

[emoji38]
 

Reply to Does freezing cold temps mean bad IR values ? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock