Discuss Does removing a socket lower breaker amperage? in the UK Electrical Forum area at ElectriciansForums.net

TheBotman

DIY
Reaction score
1
I tried removing a socket. I turned off the power, I snipped the wires off, covered with electrical tape, put those plastic twist nobs on the end each wire individually. Then tucked it all into the "socket hole. I have a plastic cover with no holes i'll be screwing over to cover the whole job.

When i turned the power back on the hallway had no power. I checked the breaker and it was in the tripped position and would not click off. So i assumed it was broken and went to the store and bought a 15 amp two pole breaker and replaced it. I turned the power back on then flipped the breaker and the red wire sparked and instantly tripped. I turned it off and came here for advice.

did i do something wrong with removing the socket? Does that lower the amperage so i need to switch the breaker size?
is there a certain method i need to follow to tuck the wires in the old socket? should i remove the whole socket compeltely and just plaster over the wall?
 

Attachments

  • pic.jpg
    239.5 KB · Views: 49
I tried removing a socket. I turned off the power, I snipped the wires off, covered with electrical tape, put those plastic twist nobs on the end each wire individually. Then tucked it all into the "socket hole. I have a plastic cover with no holes i'll be screwing over to cover the whole job.

When i turned the power back on the hallway had no power. I checked the breaker and it was in the tripped position and would not click off. So i assumed it was broken and went to the store and bought a 15 amp two pole breaker and replaced it. I turned the power back on then flipped the breaker and the red wire sparked and instantly tripped. I turned it off and came here for advice.

did i do something wrong with removing the socket? Does that lower the amperage so i need to switch the breaker size?
is there a certain method i need to follow to tuck the wires in the old socket? should i remove the whole socket compeltely and just plaster over the wall?
Did you take the time to take a picture of the 'before'? @Megawatt is one of our stateside members that may be able to advise.
 
How was the original socket wired? Ie were both the whites in the same hole, and both the blacks in a separate terminal?

If so, you will need to ensure these are still connected white to white and black to black.

you’ll need to strip a short length of insulation off the cut end, and twist the copper off the two wires together, then screw the plastic thing onto them.
There shouldn’t be any excess bare copper showing that could inadvertently touch the metal box.
The bare ground wires should also be twisted together.

Agree with above that @Megawatt is the member to advise properly
 
How was the original socket wired? Ie were both the whites in the same hole, and both the blacks in a separate terminal?

If so, you will need to ensure these are still connected white to white and black to black.

you’ll need to strip a short length of insulation off the cut end, and twist the copper off the two wires together, then screw the plastic thing onto them.
There shouldn’t be any excess bare copper showing that could inadvertently touch the metal box.
The bare ground wires should also be twisted together.

Agree with above that @Megawatt is the member to advise properly
Thank you so much for the reply. I think i understand.

White to white, then top it. Black to black then top it. Then REMOVE the bare copper wire completely.
 
How was the original socket wired? Ie were both the whites in the same hole, and both the blacks in a separate terminal?

If so, you will need to ensure these are still connected white to white and black to black.

you’ll need to strip a short length of insulation off the cut end, and twist the copper off the two wires together, then screw the plastic thing onto them.
There shouldn’t be any excess bare copper showing that could inadvertently touch the metal box.
The bare ground wires should also be twisted together.

Agree with above that @Megawatt is the member to advise properly
the socket had 2 screws for each color in total 4 connected. 2 white 2 black
 
Did you take the time to take a picture of the 'before'? @Megawatt is one of our stateside members that may be able to advise.
this is a zoomed in bad pic but i'm 95%sure those are the white connectors.

I don't know if this makes a difference of not but another plug in my house has the same configuration. 4 plugs/screws 4 wires.
 

Attachments

  • p2.jpg
    70.6 KB · Views: 42
Were the receptacles wired separately and if so had the linking tab been removed from between the terminals.
 
I tried removing a socket. I turned off the power, I snipped the wires off, covered with electrical tape, put those plastic twist nobs on the end each wire individually. Then tucked it all into the "socket hole. I have a plastic cover with no holes i'll be screwing over to cover the whole job.

When i turned the power back on the hallway had no power. I checked the breaker and it was in the tripped position and would not click off. So i assumed it was broken and went to the store and bought a 15 amp two pole breaker and replaced it. I turned the power back on then flipped the breaker and the red wire sparked and instantly tripped. I turned it off and came here for advice.

did i do something wrong with removing the socket? Does that lower the amperage so i need to switch the breaker size?
is there a certain method i need to follow to tuck the wires in the old socket? should i remove the whole socket compeltely and just plaster over the wall?
Yes you should not have taken all the wires loose. Put the whites back together, blacks and red wires. Some how you have your live wire tied in with the whites. By removing that socket you failed to consider the loads down stream. Go to Lowe’s and buy a non contact voltage checker and find that live wire
 
Then REMOVE the bare copper wire completely.

NOOOO! The bare copper wires are the grounds. They must be connected together as before. He meant don't leave any bare copper showing on the white and black wires where they enter the wirenuts.
 
Yes you should not have taken all the wires loose. Put the whites back together, blacks and red wires. Some how you have your live wire tied in with the whites. By removing that socket you failed to consider the loads down stream. Go to Lowe’s and buy a non contact voltage checker and find that live wire
Yes you should not have taken all the wires loose. Put the whites back together, blacks and red wires. Some how you have your live wire tied in with the whites. By removing that socket you failed to consider the loads down stream. Go to Lowe’s and buy a non contact voltage checker and find that live wire
Ok so this is what i'm dealing with right now. The yellow capped black wire is the live wire.

From what i understand you want me to connect the two white wires?
Then what after this?

Just so everyone knows i really appreciate the help and i will not be doing anymore work until i know 100% what to do.
 

Attachments

  • Inkedt_LI.jpg
    322.5 KB · Views: 23
Ok so this is what i'm dealing with right now. The yellow capped black wire is the live wire.

From what i understand you want me to connect the two white wires?
Then what after this?

Just so everyone knows i really appreciate the help and i will not be doing anymore work until i know 100% what to do.
Tie your whites back together, then tie your blacks together and as @Lucien says do not get rid of your bare wires they are your equipment ground, just tie them together also
 
Ok so this is what i'm dealing with right now. The yellow capped black wire is the live wire.

From what i understand you want me to connect the two white wires?
Then what after this?

Just so everyone knows i really appreciate the help and i will not be doing anymore work until i know 100% what to do.
What is that tiring them 2 black wires together
 
What is that tiring them 2 black wires together
The black wires were seperate. I put black tape on the bronze ground if that is what you are refering to.



But i think i got this now. I'm basically just putting the original wire back together to complete the current so it can travel to the rest of the fixtures and then back to the box to complete a "circuit"?
 

Attachments

  • sdf.jpg
    447.1 KB · Views: 11
  • Inkedsdf_LI.jpg
    440.7 KB · Views: 11
The black wires were seperate. I put black tape on the bronze ground if that is what you are refering to.



But i think i got this now. I'm basically just putting the original wire back together to complete the current so it can travel to the rest of the fixtures and then back to the box to complete a "circuit"?
I’m proud of you, we all knew that you would get it eventually
 
I recommend that you get an outlet tester, unplug all appliances from the outlets on this circuit, and test the outlets downstream of this point to confirm the ground is present. Plug-in outlet testers are not 100% reliable as a test method but it's better than nothing.
 
The black wires were seperate. I put black tape on the bronze ground if that is what you are refering to.



But i think i got this now. I'm basically just putting the original wire back together to complete the current so it can travel to the rest of the fixtures and then back to the box to complete a "circuit"?
As @Lucien says, you can go to Lowe’s or Home Depot and purchase this plug in tester he’s talking about and it’s less than $ 10.00 good luck
 
I recommend that you get an outlet tester, unplug all appliances from the outlets on this circuit, and test the outlets downstream of this point to confirm the ground is present. Plug-in outlet testers are not 100% reliable as a test method but it's better than nothing.
@Megawatt @Lucien Nunes
As @Lucien says, you can go to Lowe’s or Home Depot and purchase this plug in tester he’s talking about and it’s less than $ 10.00 good luck
Thank you for all of your help.
I pluged everything together. The grounds seemed to be connected in the back by two screws for each end

All my lights are back on, the connections don't seem to be smoking or sparking lol. and everything seems to be working as normal. I'll keep a close eye on it for the next couple of days while i do some more plastering and painting.

Turns out I called the previous owner of the house and the one circuit breaker i thought was tripping the back hall, was actually a totally different area of the house. An old water tank. So i just flipped it off and put tape on it to remember not to flip it. I'll be switching out the whole circuit board next as i found out its outdated Sylvania......


Again thanks everyone for your feedback and help.
 
@Megawatt @Lucien Nunes

Thank you for all of your help.
I pluged everything together. The grounds seemed to be connected in the back by two screws for each end

All my lights are back on, the connections don't seem to be smoking or sparking lol. and everything seems to be working as normal. I'll keep a close eye on it for the next couple of days while i do some more plastering and painting.

Turns out I called the previous owner of the house and the one circuit breaker i thought was tripping the back hall, was actually a totally different area of the house. An old water tank. So i just flipped it off and put tape on it to remember not to flip it. I'll be switching out the whole circuit board next as i found out its outdated Sylvania......


Again thanks everyone for your feedback and help.
You are welcome and that’s what we’re here for
 

Reply to Does removing a socket lower breaker amperage? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I'm not an electrician. I clean cookers and today arrived to a rangemaster range cooker. Got started, and as part of my routine, I turn on ovens...
Replies
1
Views
837
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
820
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
869
We have one room that seems to have lost most of its power last night. One of the outlets in the rooms has a power strip plugged in that powers...
Replies
5
Views
837
Woke up this morning and tried to turn on the computer (work from home) wouldn't power on, checked lights they worked fine. Went downstairs to...
Replies
21
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock