Discuss Does this metal post need to be earthed or bonded or neither? in the UK Electrical Forum area at ElectriciansForums.net

HappyHippyDad

-
Esteemed
Arms
Reaction score
5,607
I have 5 x 6m metal posts sticking out of the ground used for 200w floodlights to light up a manege.

This is a domestic stables. The posts test as 35ohms to earth. The installation is TNCS and has 30mA RCD protection on all circuits.

The floodlight will be earthed and in doing so the post will become earthed as the bracket holding the floodlight to the post is metal.

I just cant quite work out if the post is an extraneous conductive part and needs a 10mm bonding cable or if it's an exposed conductive part as it's housing the cable up the middle of it and is holding the light, in which case it is earthed, however is the 1.5mm earth feeding the floodlight sufficient.

The cable feeding the arena lights is 6mm 3 core SWA.

Just when i think I've got earthing and bonding completely sussed I get a situation that confuses me!
 
ok, so the post on its own is no risk to anybody.
just a metal pole sticking out of the ground.

there is no risk of someone being in contact with the earth to light fitting and a different potential earth from the post itself.
I presume the circuit is rcd protected?

personally I cant see an issue.
it would seem ridiculous in my mind to bond the posts with a 10mm cable.

I am happy to wait for constructive criticism if my interpretation is incorrect.
 
I'd say it would be an exposed conductive part at most as it's forming part of the electrical system. but if unsure IR test to earth and if greater than 0.02mohms it's just a piece of metal
It's measured 35ohms to earth so just a tad under 0.02Mohms :)
There is a weatherproof junction box 40cm above the base of the post (attached to the post) which houses the terminations going up to the floodlight and on to the next post.
 
IMO as long has it has a connection to a cpc and the entire length of the cable that is in contact with the pole is 30mA rcd protected. you don't need to take a main bond to it..

If it wasn't RCD protected before coming in contact with the pole then it would require bonding.
 
IMO as long has it has a connection to a cpc and the entire length of the cable that is in contact with the pole is 30mA rcd protected. you don't need to take a main bond to it..

If it wasn't RCD protected before coming in contact with the pole then it would require bonding.

If the metal work becomes live due to a broken PEN conductor how will an RCD affect the outcome ?

In my opinion you should insulate the physical connection between the floodlight bracket and the post .
 
By connecting the TN-C-S earth to the post, you could create a voltage gradient from the post across the soil, since the TNCS PEN could be a significant voltage away from true earth. It won't be much of a gradient because of the low Ra of the post, however horses are very sensitive to voltage gradients. It might be better to isolate the post and/or fitting from the supply earth.

Post crossed with Jim's
 

Reply to Does this metal post need to be earthed or bonded or neither? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

As above the chest level from ground ,metal ANPR housing has no connection to earth ,it has monitors modems and a camera inside with a 230 volt...
Replies
2
Views
681
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K
In a communal electric intake room for flats (meter room) there is lots of bonded trunking and tray, also the metal door frames were found to have...
Replies
1
Views
748
I have just put in a sub distribution board in the middle of a field for a new supply for some poly tunnels (soil heating mats and lighting). I...
Replies
41
Views
4K
Good morning everyone. I’m looking at getting an EV charger installed at my home and the company is requesting that I earth bond my water supply...
Replies
8
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock