Well an FCU contains an OCPD (Fuse).
If I use an FCU to spur off from a circuit, does the fact that there is an OCPD at the origin of the spur, make the spur a separate circuit?
Where does the supply originate from?
The circuits primary OCPD.
Why twist things and be argumentative as per?
 
Ok where’s the OCPD at the origin of an installation?
That depends on how far back to “origin” you want to go? The MCB is an OCPD if it’s an origin of a final CCT. The bs1361 or 88-3 fuse is An OCPD if it’s the origin of a particular installation. The substation fuse, the grids fusing all the way back to the OCPD at the generator...
 
That depends on how far back to “origin” you want to go? The MCB is an OCPD if it’s an origin of a final CCT. The bs1361 or 88-3 fuse is An OCPD if it’s the origin of a particular installation. The substation fuse, the grids fusing all the way back to the OCPD at the generator...
The distribution network is outside of the scope of BS7671.
As the discussion is in relation to an Assessor stating something does not comply with BS7671, I was thinking of the origin as per BS7671.
 
I'm also interested in why markysparky disagreed with sparkychick's post re lollipop circuits.


Because, as Spin helpfully points out, details on how a circuit is formed is in appendix 15. And as we seem to be so intent on dissecting the regs to the nth degree, there is nothing at all that looks remotely like a ‘lollipop’ circuits in app15. Therefore, if it is not in the regulations of how a circuit should be wired, it is not compliant.
 
The regs cannot possibly show every possible circuit. I presume you would class any lollipop ring you come across as unsatisfactory then?
 
The Appendix 15 argument.

Appending 15 is informative only, it doesn't matter how many times people claim it is a regulation, it isn't, it's there in black and white (INFORMATIVE).

The opening text reads "This appendix sets out options for the design of ring and radial final circuits for household and similar premises in accordance with Regulation 433.1"

Options... it is not the exhaustive list of possibilities that comply with 433.1, if it were some of what we do everyday would be non-compliant (like a 20A DP switch feeding a single socket for an appliance wired in 2.5/1.5mm cable - complies with 433.1.204 but isn't on the diagram in appendix 15).

For a ring circuit to comply with the regulations, it must comply with 433.1.204 which defines the acceptable topology of a ring final circuit purely in terms of cable loading. Thus providing the cables are not overloaded in accordance with 433.1.204, a lollipop or ring final circuit will comply.
 
The regs cannot possibly show every possible circuit. I presume you would class any lollipop ring you come across as unsatisfactory then?

If course! A C3 if I were doing an EICR.

And how can it be a lollipop and also a ring? What would you put under the continuity tests in an EIC and also if the ‘stick’ end is of a larger size what size cable do you put in the EIC?
 
The Appendix 15 argument.

Appending 15 is informative only, it doesn't matter how many times people claim it is a regulation, it isn't, it's there in black and white (INFORMATIVE).

All the appendixes are informative with the exception of the appendix 1.

The opening text reads "This appendix sets out options for the design of ring and radial final circuits for household and similar premises in accordance with Regulation 433.1"

It sets out the ‘options’ by indicating what can be done and what is acceptable.

Options... it is not the exhaustive list of possibilities that comply with 433.1, if it were some of what we do everyday would be non-compliant (like a 20A DP switch feeding a single socket for an appliance wired in 2.5/1.5mm cable - complies with 433.1.204 but isn't on the diagram in appendix 15).

Where does it say that it’s not exhaustive?

For a ring circuit to comply with the regulations, it must comply with 433.1.204 which defines the acceptable topology of a ring final circuit purely in terms of cable loading. Thus providing the cables are not overloaded in accordance with 433.1.204, a lollipop or ring final circuit will comply.


I’ve said all through this thread ‘loads accepted’ or ‘loads considered’. Lets drop this part as I have accepted this. My argument is not about this, only the make up of a circuit and where it starts.

I have said on numerous occasions that two or more circuits that are lumped together in a protective device is not necessarily electrically unsafe, but just that it doesn’t comply.
 
Yes Appendix 15 is informative.
It provides us with information.
It’s not the be all and end all, but there is no logical reason why the information provided should be ignored.
(Except of course when it states a Radial starts and finishes at the DB.)
 
Appending 15 is informative only, it doesn't matter how many times people claim it is a regulation, it isn't, it's there in black and white (INFORMATIVE).

All the appendixes are INFORMATIVE with the exception of app1.

The opening text reads "This appendix sets out options for the design of ring and radial final circuits for household and similar premises in accordance with Regulation 433.1"

It sets out the 'options' (something that may be chosen) of how to wire a type of circuit. It does not give 'examples' (one of a number of things or a part of something, an instance serving for illustration). If it could be wired like a lollipop it would have a diagrammatical representation of this too!

Options... it is not the exhaustive list of possibilities that comply with 433.1,

Where does it say that?
 
The regs can't possibly show every possible wiring configuration. And they don't need to - a competent electrician does not need to follow a guide covering every option. wiring installations can still comply with the regs even if they aren't specifically drawn in the book!
 

Reply to Does this setup contravene any regs or is it ok? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
446
We are in the process of renovating our house, and would like to setup led strip-lighting throughout. of the options, this seems most attractive...
Replies
4
Views
749
I’ve recently moved into house and had an electrician out to install some new lights and shaver point in an en-suite. Problem is that the house is...
Replies
16
Views
1K
Hi all, Looking for someone to help with this dilemma. Image attached to try and explain it better. We have 3 separate lights currently...
Replies
3
Views
614
I'm getting an old fuse board upgraded in an office block. The electrician has just told me that most of the circuits don't have earth cables...
Replies
44
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock