Discuss Domestic three phase? advice in the UK Electrical Forum area at ElectriciansForums.net

Jay

-
Reaction score
4
Hi

I have recently moved into a small newly renovated (inc electrics) cottage and noticed appliances going really slow. Kettle taking an age to boil, toaster taking a long time, hair clippers going slow... you get the picture.

UK power networks sent an engineer that changed the overhead power line. He monitored the voltage at the plug sockets with no load and was getting 216v. He advises to get an upgrade to three phase.

Move forward to the site survey. A new technician says Three phase is not required on such a small property and that UKPN will need to get a monitor installed temporarily to monitor the incoming voltage.

UKPN customer services are not having any of that and are insisting it does require a Three Phase upgrade going against the site survey technician.

It is worth noting the house only has electricity (no gas) including an electric combi-boiler. We have overhead power lines and we are the furthest house on the street from the supply.

Another technician is due out next week for another survey.

As you can probably tell I am no expert so any advice would be very welcome. Is three phase usual on a small domestic property?

Thanks.
 
To be honest i'm not sure. It's probably worth knocking and asking.

What I don't want is to be in a position of paying for an upgrade that may not be necessary.
 
Have they put in monitoring equipment. According to the Electricity Safety, Quality & Control Regulations 2002 there is some tolerance on the quoted nominal voltage of 230v, this being -6% and +10% which equates to a range of 216.2 to 253v so you could argue yours falls outside this.
 
The monitoring equipment is what I am trying to push for. Hopefully the new survey will point in the same direction as the first.
 
Thanks for the replies. Yes i will push for the monitoring equipment and go from there. Fingers crossed they will sort it if its below the minimum requirements (i wont hold my breath tho :).
 
I had this exact problem however my experience with UKPN was pleasant. Long story short, a car park was complaining that their flourescent lights dimmed at certain times, we put our own monitoring equipment on and saw the voltage rapidly decrease to about 216V. Across all phases too.
We passed the info to UKPN and they fixed the fault in 48 hours and said it was due to football floodlights and the local train station.
Hopefully your issue will be resolved soon! It could be a range of issues but if you can see a trend in the time then it could be fluctuating Voltage due to heavy loads.
 
UK power networks sent an engineer that changed the overhead power line. He monitored the voltage at the plug sockets with no load and was getting 216v. He advises to get an upgrade to three phase

I'd love to hear their logic behind this.
 
it looks like a heavily loaded local electrical network,
or your at the end of a long line.
either way it's the network not the equipment.
Try reporting low voltage and request more capacity ?
(bigger local transformer).
 
Maybe,just maybe,the DNO is aware of this issue,but rectifying it,could involve multiple customers,and a large expenditure...but...a 3 phase connection,from a nearby sub-terra supply,would avoid this,and,because offering this for free,would flag the aforementioned problem,an invoice is obligatory...

Purely conjecture,and,obviously,this has never,ever,happened before...:rolleyes::rolleyes::rolleyes:
 

Reply to Domestic three phase? advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I'm new to this forum, we are in the process of converting into 12 flats all electric, no gas incl. heating, showers etc. An electrician...
Replies
10
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
Hello, I've been trying to find some information on split-phase today but not having much luck which brings me here. We're moving house to quite...
Replies
6
Views
3K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
(Thought I'd already poost this Q, but I cant see it, so I'll try again) We have some work going on in one of our buildings atm. On of the chaps...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock