Just bought a xpelair 12v humidistat 100mm fan to go in zone 1 and reading instructions it asks for a d/p switch. Is that the regs ? I assumed it could be wired as normal i.e. live from light switch and perm live etc .. having looked into it a bit more it seems i could go 230 v if rcd protected (which it is ) but unsure if wise to ?? I'm a 16th edition sporadic sparky a little confused...
 
Are you replacing an existing fan or putting in the circuit for a new one, if the latter it will need additional rcd protection. The fan can be 230v as long as it is suitably IP rated and installed as per manufacturers instructions.
 
Reg 537.2.1.1 requires each of the live supply conductors to be isolated, except in TN-S or TN-C-S, although manufacturers instructions should be taken into consideration. Most bathroom fan installs, use TP fan isolating switch, so you isolate the fan for maintenance, without having to disconnect the supply to the light (if you have no window, or you like cleaning in the dark), and some customers like to turn them off at night for some reason!

If the fan is a new addition in your bathroom (not a replacement), it would now need RCD protection. If the fan is installed in Zone 1, it would need to be IPX4 or IPX5 if it could splashed by water jets (e.g. shower head). As regards low voltage or extra low voltage, as long as you comply with IP rating, that's your decision.

PS If it is a new fan installed in Zone 1, it should be (cough), notified to LBC.
PPS Humidistat fans, don't get good press on this forum.
 
Thanks for quick replies. First time on any forum ever... impressed!

Yes its a new consumer unit rcd etc and yep LBC involved ! From memory its TN-C-S.
I should add I'm renting the flat out so leaning towards 12 v just to be safe but if it meant i didn't have to provide a separate d/p switch maybe i would go 230v just feels a bit dodge !

My ideal would be a 12v fan that operates as mentioned before - off the light switch. The humidistat is to hopefully keep the small ensuite wet room ventilated if they (the renters) don't turn light on. Sounds like i should be buying a good quality unit if they are problematic ... thanks
 
Installing isolators for fixed equipment has been normal practice for a long long time hasn't it?

And what on earth is a 16th edition electrician supposed to be?
 

Reply to double pole switch on a bathroom selv fan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
1K
Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
621
hello all, pardon my ignorance in not employing an electrician, however, im a diy'er whos changing the light switches in my house and came across...
Replies
11
Views
2K
Hi, I've just had some electrical work completed in the bathroom; I've recently refurbished the bathroom, replacing the old electric shower with...
Replies
39
Views
8K
Hi I have a double pole switch that switches on and off the outside lights under guttering area (front side and rear of the house all operated by...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock