Hi there sorry if I’m not making myself clear from the title, I live in a bungalow.

basically I want to add a double socket in the attic with the ability to turn it on and off from my passageway just below the attic door,

would this be possible by adding a switch to my existing light switch ?
 
For a start a socket should not be off a light circuit!

It would also be very unwise to mix two circuit supplies on one switch, and most light switches are only rated at 10A anyway which is inadequate for a 13A socket as you can see.

Safest option should you later want some more outlets in the attic, but are happy with a total of 13A is to use a fused switch from the usual ring circuit that the rest of your sockets are using. If you want it to be obvious when it is on then you can get such switches with a neon indicator to show when they are powered:

If in any doubt ask a professional electrician to come and sort it out. They will also do full testing of the resulting sockets to make sure they are safe.
 
Hi there sorry if I’m not making myself clear from the title, I live in a bungalow.

basically I want to add a double socket in the attic with the ability to turn it on and off from my passageway just below the attic door,

would this be possible by adding a switch to my existing light switch ?
Unfortunately not, for multiple reasons, but the main one being that lighting circuits are generally lower power (6 Amp) circuits, and sockets need more like 13+Amps.

Is there a socket nearby on either side of the wall? It may be possible to take a feed from that up through a fused spur (which looks something like a light switch but has a fuse in it). That would need to be done by someone who can safely do the work though.
 
What do you want to power from the double socket?
Easily done mate like the previous spark said supply from socket into 13A switched fused spur. Then from the load side of that spur take cable up into attic and if you want a light up there incorporate another fused spur with 5A or 3A fuse in there rather than the 13A and jobs a good un ?
[automerge]1599868637[/automerge]
Easily done mate like the previous spark said supply from socket into 13A switched fused spur. Then from the load side of that spur take cable up into attic and if you want a light up there incorporate another fused spur with 5A or 3A fuse in there rather than the 13A and jobs a good un ?
Aslong as your not growing you’re tomatoes up there? ?
 

Reply to Double socket in attic, ability to turn on off downstairs? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Got an awkward bathroom fan installation in a downstairs flat, concrete ceilings and (some) walls. Bathroom is already fully tiled and...
Replies
1
Views
611
Hi, i live in a new build house where they builders have left a junction box on the outside of my house. In the junction box there is a 6mm twin...
Replies
14
Views
1K
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
408
Hi, I live in Houston TX and my house was built in 2000. In my attic, I had a dual socket electrical outlet. My tankless water heater was...
Replies
0
Views
1K
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
840

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock