723
My colleague asked me earlier if it was possible to fit different panels to an inverter that had a two MPP trackers - for example a string of 10 Sharp 185s on one MPP tracker and another string of 7 Sharp 245s on another?

I didn't know so I thought I'd ask on a forum where someone probably does.
 
Niether sunny design or PV*Sol let you run that configuration, I tried almost the same config myself but gave up and used Romag 185 panels instead!
 
i would agree with dansk. each MPP tracker is to all intents and purposes a seperate inverter. why would one know about what the other was doing?
 
There shouldn't be a problem at all so long as it is an inverter with proper twin MPP trackers, (SMA, Fronius ...) it's just two different strings with different characteristics just like orientation, shading, slope etc.

Some of the cheaper inverters seem to have pseudo twin MPP's (one MPP controlling seperate inputs).

Both PV*Sol and Sunny Design happily let you model this configuration (PV*Sol, One system inverter, multiple arrays), and the results are fine.

Sunny Design, Set up the two arrays, choose an inverter, manually configure the strings to match the panels installed
 

Reply to Dual MPP tracker inverter - two different panels? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello All, I'm seeking some advice about a solar PV system we had installed in November 2014 please. After 18 months, we seem to be consistently...
Replies
15
Views
6K
crossplot
C
N
Hi All, thanks for taking the time to read this!! I'm currently trying to decide on a solar PV system to get installed on my house. I've a...
Replies
6
Views
2K
macca499
M
I just had a 4kW system installed. It uses the Samil Solarriver 4000TL-D inverter which has 2 DC inputs. There are 2 strings of 8 panels, each...
Replies
30
Views
7K
K
Just wondered how it is possible to register and installation with a variety of panels? For example, with solar edge / micro inverters you can...
Replies
3
Views
1K
ktech
K
A pretty fundamental question I have here.... I was under the impression that the effects of shading could be negated slightly by using seperate...
Replies
9
Views
8K
PV Martin
P

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock