fire8789

Hi guys, looking for abit of help.
Carried out a consumer unit change today, carried out all dead testing etc, all came back ok.

New board is a twin 63a RCD.

With the following configuration both RCDS tripped straight back out.

RCD 1 *upstairs lights
*Downstairs sockets
*Boiler
*Bathroom Low voltage


RCD 2 *Downstairs lights
*Upstairs sockets
*Cooker
If I swapped the upstairs lights over to RCD 2 however + then swap the downstairs lights to RCD 1 there were no problems.

I did find some kind of neutral interconnection via insulation resistance testing between upstairs and downstairs light circuits. which came back as 0.03 ohms.

Any ideas as to whether this would cause the RCDS to trip as described above and if so what the best possible way of tracking the fault would be?

Any help would be much appreciated.

Regards. Rich
 
it sounds like a shared neutral. investigate that 0.03 ohms for a start, or was it 0.03 megohms?
 
agree with Tel....shared neutral....
IR test between em.....that`l find it....
likely to be the up hallway lighting.....
this will be using the down lighting phase....and the upstairs neutral.....
it aint cast in stone that this is where it is.....but likely....
 
cheers for the replies guys,
Hi trev, I am fairly new to this. I carried out my IR tests on individual circuits so the link between the up and down lights wasn't found until the cu was connected.
Is it normal procedure to IR test between seperate circuits to rule this sort of thing out?
 
Normally you'd do a few tests first before swapping over the CU. Global IR, test between lighting circuits to identify borrowed neutrals, EFLI etc. This is to make sure there's no nasty surprises waiting for you that will make your shiny new RCD go bang.
Didn't they tell you this?
 
cheers for the replies guys,
Hi trev, I am fairly new to this. I carried out my IR tests on individual circuits so the link between the up and down lights wasn't found until the cu was connected.
Is it normal procedure to IR test between seperate circuits to rule this sort of thing out?


Yes, after its happened to you a few times!

and a global N-E IR test.
 
Yes I carried out what I thought to be all the neccessary checks, basically running through the schedule of test results sheet.
ZE, PFC at DB. Earthing type, Continuity, then IR on induvidual circuits.
I thought this was all that was required before a cu change...

sorry if this is frustrating for you guys, but I can't see how a global IR test would indicate that there is a problem between two neutrals as the neutal bar and earth bars are left untouched arent they?
 
A global IR wouldn't show it but would show up anything IR related that could bite you on the ---. The test between lighting circuits would have shown the borrowed neutral though.
 
Yes I carried out what I thought to be all the neccessary checks, basically running through the schedule of test results sheet.
ZE, PFC at DB. Earthing type, Continuity, then IR on induvidual circuits.
I thought this was all that was required before a cu change...

sorry if this is frustrating for you guys, but I can't see how a global IR test would indicate that there is a problem between two neutrals as the neutal bar and earth bars are left untouched arent they?
you IR between neutrals on finals......and that certainly would show up anything shared.....
thats why we do it....
its common on older installs.....
 
There are a couple of points to raise.

The OP said that when the two lighting circuits were swapped to the other RCDs the problem disappeared.
This would indicate a link between one of the lighting circuits and another circuit which is now on the same RCD.

Also, 0.03MΩ which could actually be anything between 0.025 and 0.0349 is not enough on its own to trip a 30mA RCD.
245/25,000Ω (worst case) = 9.8mA
 
If a neutral is borrowed at the top landing light (most common I've come across), it is normally taken from a bedroom light or whatever nearby - the problem you will have identifying this is that it's only electrical connection to your downstairs circuit is through the landing lamp then down through the phase conductor/switch etc - neutral to neutral test at board may not reveal it unless you ensure that all lamps are in and all switches are closed (P to N tests across circuits also).

Another way to check for this - clamp ammeter on neutral of one circuit (dead) while other circuit is live with all lights on - then vice versa - If you have a suspect current you can turn lights off in turn till you find the culprit.
 
Last edited by a moderator:
If a neutral is borrowed at the top landing light (most common I've come across), it is normally taken from a bedroom light or whatever nearby - the problem you will have identifying this is that it's only electrical connection to your downstairs circuit is through the landing lamp then down through the phase conductor/switch etc - neutral to neutral test at board may not reveal it unless you ensure that all lamps are in and all switches are closed (P to N tests across circuits also).

Another way to check for this - clamp ammeter on neutral of one circuit (dead) while other circuit is live with all lights on - then vice versa - If you have a suspect current you can turn lights off in turn till you find the culprit.

never tried that. will have to give this method a go sometime. as they say, every day's a schoolday.
 

Reply to Dual RCD problem (interconnection between lighting circuits?) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
781
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
331
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
608
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock